Furnace Connect G Wire

furnacehvacoilthermostat

I have a dual energy electric/oil furnace that is wired to a thermostat with 2 wires R and W. I don't have any AC. Inside the furnace there is a switch relay to control the fan but it is not connected to the G terminal inside the furnace. I would like to run a 5 wire cable from my thermostat and the furnace and connect the W R and G wires to use the Auto / On fan switch on the thermostat instead of the switch relay inside the furnace, and eventually the C wire as well.
Fan Switch ad Relay

Since the G terminal inside the furnace is not connected to anything, how can I connect it to achieve what I want?
Terminals
Disconnected terminal G, third from right

Should I bypass the manual switch or an I wire the thermostat in parallel ?

The fan relay
enter image description here

Best Answer

You need to add a relay to the system to independently operate the fan separate from the heat.

The simplest way is to buy a new high voltage 120VAC (20-30 Amp?) heavy duty relay/contactor that switches with a 24VAC control voltage and connect both relays to the high voltage circulation fan. If either relay is on the fan gets power. The existing fan relay will power the fan when you call for heat, and the new fan relay will power the fan when you call for fan only.

If you don't add a relay and still somehow hook it up, your heat will probably turn on every time it calls for fan only.