I noticed my furnace sweating a couple days ago. It's hot and humid where I live so I was only mildly concerned. It was a high of 74F today with humidity around 70% which is, relatively, nothing. My thermostat keeps the house around 72F.
Lately, I've noticed that my A/C is running 90% of the time (a lot), but chalked it up to this being the hottest month.
Side of Furnace with Sweat Drops
Good Size Water Trail on Floor
Two Small Streams Coming from the Other Side
Condensation Runoff Line
It looks slightly kinked, but has been that way since before the summer. I don't know what the blue tube is.
Just for Fun: This is How the Condensation Line Connects to the Main Sewer Line 😀
Is this bad? What could be causing this?
I've researched online and found some informal sources that say something in the airflow is being blocked/clogged somewhere…
Edit in Reply to @Tester101's Questions in the Comments:
The System as A Whole
At the bottom of that "V", where the grey and off-white metal meet, is where Picture #1
above was taken.
Inside the Upper Front Panel
I think this section only has to do with heating, but I don't know if you guys see anything useful.
The Rear Panel
It looks like I can unscrew that entire rear side, but I won't do that unless necessary. There is also a smaller panel in the top of the photo. Should I open that?
Best Answer
There are two main contributing factors at play here. First and most importantly, the evaporator is getting too cold. The other problem is only a problem, because the first problem is a problem. And that is, that the humidity in the basement may be too high.
What's happening, is that the box that contains the evaporator is getting too cold. Once it cools below the dew point, it causes the moisture in the air around it to condense. To solve the issue, you're going to have to figure out why the evaporator is getting so cold.
Improper refrigerant level
My first guess, would be that the system is not charged to the proper level. Specifically, in this case I think it may be undercharged. Though, you may also see this if it was overcharged. However, since it sounds like it hasn't always been a problem, I'd suspect the system developed a leak.
Testing
To test this, you're going to need a set of gauges. If you don't have a set; or don't know how to use them, you're going to want to contact a local HVAC company.
Restricted air flow
If not enough air is moving through the coils, the little bit of air that is there could be getting too cold.
Testing
Check the filter, to make sure it's clean. Check the evaporator coils, to make sure they are clean. These are the two most common causes of restricted air flow. Additionally, make sure registers and returns are open and unobstructed. If your system has a multi-speed blower motor, make sure it's set to run at the manufacturer's recommended speed.
Long running system
If it's really hot outside, and your system is running almost constantly. It could just be that the evaporator doesn't have time between cycles to warm up. If this is only a problem when it's abnormally hot outside, it could be "normal" for that situation. Typical A/C systems are designed to cool between 20-30°F, anything beyond that and they'll struggle to keep up.
High humidity
If everything is operating normally, but the system just happens to be in an area where the humidity is high. It might be a good idea to insulate the system, especially in the area around the evaporator. This is common when the equipment is installed in unconditioned spaces (attics, garage, crawlspace, etc.), but if your basement has moisture problems, it might be required there too.
If the moist air cannot get to the cold metal, the moisture in the air will not condense. However, if the now insulated system gets too cold, you could have problems with the evaporator freezing. So I'd only install insulation, if I was sure the system was operating normally.