G to C trick not working for cooling. Honeywell RTH9080WF

hvacthermostatthermostat-c-wire

My electric furnace has no c terminal. Furnace is heat & cool both. (Lennox Electric Fan coil Model CBS18-21-3P).

I installed Honeywell RTH9080WF.
I switched G to C on my thermostat and got the power.

Furnace has no C Terminal.
The connections on furnace is "R" "W" "G" "Y"

Further on my thermostat I chose "fan controlled by heat pump" and it worked. Heating worked for the whole season.

In summers I switched to cooling and found that compressor is coming up but fan is not.

Fan comes up with heating but does not work with compressor.
Kindly advice how to fix this problem.

Best Answer

Your original wiring looked like this, where the top circles represent the thermostat terminals and the bottom the furnace.

enter image description here

To properly pull off the "G wire trick", you have to locate the transformer in the furnace. You then have to determine which leg feeds R, and which does not. The leg that does not feed R, will be where you connect your new C wire.

enter image description here

Once you have all that hooked up, then you'll install a jumper between the Y and G terminals in the furnace.

enter image description here

Once all that is completed, you'll have to make sure the motor is spinning at the correct speed when in cooling mode. If it's not, you'll end up with inefficient cooling. Which can cause poor performance, and/or damage to the system.