look at page 22 of the manual: http://www.heatilator.com/downloads/installManuals/4031-551.pdf
using a multimeter, check the voltage being sent to the valve while the fireplace is on, which should be the green and orange wires. the re-check it after you turn it off and the pilot is still on. if the on and off voltages are different, then your gas valve is faulty. if the voltages are the same, then your controller is faulty.
if the it's valve, do not replace it yourself. in nearly every jurisdiction, it is illegal for non-licensed people to do work on gas fixtures.
note that it might also be that you just never noticed that the pilot remains on for a brief time as it burns the residual gas in the line.
It's difficult to help you troubleshoot a device, without a bit more information about it. Since you're not giving us much, I'll try to give general advice.
Depending on the system, there's a few things that could be wrong.
Gas Valve Closed
This would affect every type of gas fireplace.
Test:
- Locate the gas valve.
- Turn on the switch.
- Listen for the valve to open.
If you hear the valve open (click, clank, clunk, etc.), but don't hear or smell gas. The valve may be off.
Most gas valves are quarter turn ball valves, so you can tell when they're open simply by looking at the knob. The knob should have an arrow, handle, or other linear feature on it. This feature should be aligned with (parallel to) the pipe, when the valve is open.
Solution:
Turn on the gas.
No Gas
If you get your gas from a tank or bottle, you'll want to make sure you have gas.
Test:
Similar to above, except that the valve will be open.
Solution:
Fill the tank.
Bad Switch
Since the system relies on a switch to know when to turn on, a bad switch could be devastating.
Test:
- Label and remove the wires from the switch.
- Test continuity across the switch, in both positions.
When the switch is toggled on way, you should measure infinity (or not hear a beep). When the switch is toggled the other way, you should get a measurement (or hear a beep).
Solution:
Replace the switch.
Pilot Not Lit
If your system requires a pilot, and it's not lit. You can flip the switch all you want, you'll never make fire.
Test:
- Look at the pilot.
If you see a flame, it's lit.
Solution:
Light the pilot.
Bad Flame Sensor
Fireplaces use flame sensors (thermocouples, thermopiles, etc.), to determine if there's a flame. If the sensor goes bad, the system will not hold the gas valve open.
Test:
- Disconnect the thermocouple from the system.
- Set multimeter to measure DC millivolts (mV).
- Connect the black lead to the button of the thermocouple.
- Connect the red lead to the copper part of the thermocouple.
- Heat the thermocouple with a torch.
As the thermocouple heats, you should get a reading on the multimeter.
Solution:
Replace the flame sensor.
Bad Gas Valve
If the system is getting all the right signals, but the gas valve is not opening. It could be a bad valve.
Test:
See test for Gas Valve Closed. You won't hear the valve open. You'll have to be sure the valve is getting the signal to open, so make sure all other items check out first.
Solution:
Replace the valve.
Depending on the type of fireplace, the ignition sequence will be a bit different. using the typical sequences below, you might be able to narrow down where the problem is.
Typical Gas Fireplace Ignition Sequence
Pilot
- Switch is flipped
- If pilot is lit (checked via a thermocouple or other flame sensor).
- Open main burner gas valve.
- Wait (There may be an adjustable timeout, or a hard set timeout).
- If main burner lit (check via another thermocouple or other flame sensor).
- Leave main gas valve open.
- Else
- Close main gas valve.
- Purge system (in the case of a fireplace, this is likely a timed wait).
- Retry ignition (this may happen 0 to many times, depending on the system).
- Else
Electronic Ignition with pilot
- Switch is flipped
- Open pilot gas valve.
- Initiate electronic ignition device (spark gap, hot surface, etc.).
- Wait.
- If pilot flame sensed.
- Open main burner gas valve.
- Wait.
- If main burner flame sensed.
- Hold main gas valve open.
- Else
- Close main gas valve.
- Purge system.
- Retry ignition.
- If no ignition after retries
- Close pilot gas valve.
- Lockout (this may require something to be physically reset, or a simple timed lockout).
- Else
- Close pilot gas valve.
- Purge system.
- Retry ignition.
- If no ignition after retries
- Close pilot gas valve.
- Lockout.
Electronic Ignition
- Switch is flipped
- Open main burner gas valve.
- Initiate electronic ignition device.
- Wait
- If flame sensed.
- Hold main gas valve open.
- Else
- Close main gas valve.
- Purge.
- Retry.
- Lockout.
Best Answer
Gas , oil, and wood need air( oxygen) to burn , then the flue gas can be vented. So , let in some air, A K A -open a window. When I lived in a colder climate , I always provided an air inlet , generally a duct pipe from outside to near the furnace, or fireplace in this case. Newer furnaces are generally required to have an ejector fan on the exhaust vent because newer houses are well sealed and it is difficult for a natural draft to work. The lower the outside temperature , the more the problem.