I have a concrete slab which can fit a hot tub approximately at a distance of 8 feet from the main breaker panel (located outside on my porch). I assume that I will still need a separate disconnect for the hot tub (minimum of 5 ft from the tub). Can I just pop the disconnect box (with GFCI breaker and 120V outlet) directly next to the main breaker box and then run my #6 cables from there to the hot tub (~20 ft total)? Or does the disconnect need to be separated from the main for some reason? Thanks!

-Phil

Best Answer

The pertinent parts of Article 680 I have quoted here:

680.12 Maintenance Disconnecting Means One or more means to simultaneously disconnect all un-grounded conductors shall be provided for all utilization equipment other than lighting. Each means shall be readily accessible and within sight from its equipment and shall be located at least 1.5 m (5 ft) horizontally from the inside walls of a pool, spa, or hot tub unless separated from the open water by a permanently installed barrier that provides a 1.5 m (5 ft) reach path or greater. This horizontal distance is to be measured from the water’s edge along the shortest path required to reach the disconnect.

680 Part IV. Spas and Hot Tubs 680.40 General Electrical installations at spas and hot tubs shall comply with the provisions of Part I and Part IV of this article.

680.40 refers to Part I and the requirement for a disconnect is in Part I (630.12).

This commentary is from the 2011 NEC Handbook:

A readily accessible disconnecting means is required to be located within sight of pool, spa, and hot tub equipment in order to provide service personnel with the ability to safely disconnect power while servicing equipment such as motors, heaters, and control panels. Underwater luminaires are not subject to this requirement. The proximity of the disconnecting means to the pool must be not less than 5 ft unless the disconnecting means is separated from the water by a permanent barrier.

Notice here it says unless the disconnect is separated from the water by a "permanent barrier". If you have a permanent barrier such as a partition between the tub and the disconnect it can be closer than 5 feet. Otherwise 5' is your minimum distance.

So, you were reading the code correctly you need a disconnect in-sight of the spa and mounting next to the main panel will work just fine. Or using a breaker in the panel will work as you and Speedy Petey were discussing.