Wiring Diagrams
Locate the schematic
In most cases, a wiring diagram can be located inside the HVAC unit. Typically, it will be on the inside of the access cover.
Find the transformer on the schematic
Once you've located the diagram, you'll want to look for this symbol.
Or the actual text that says "Transformer", which may be labeling a crudely drawn transformer, or simply a rectangle.
Primary or secondary?
After finding the transformer in the diagram, you'll have to determine which wires are connected to the primary coil, and which are connected to the secondary coil. Check the diagram for a key, which will give you a hint. On some diagrams a thicker (bold) line denotes line voltage wiring, while a thinner line represents low voltage wiring. Others may list the voltage and frequency on each side of the transformer.
Trace the wires
Now that you know where the transformer is on the diagram, and which side is the secondary. The next step is to follow the lines, and see where they go.
In this example diagram, you can see that one leg of the secondary connects to the R
terminal on the control board, and the other leg connects to the C
terminal. In this example there's actually a C
terminal present, but that will not always be the case (especially in old models). However, even if there isn't a dedicated C
terminal, that doesn't change what the C
wire is. Which is simply the other side of the secondary coil.
In Real Life
Now that you've located the transformer in the diagram, or maybe you don't have a diagram. Either way, you'll have to locate the actual transformer inside the HVAC unit. You'll be looking for something that looks similar to this...
Honeywell 24V AT72D Transformer
An action shot of the actual transformer in my furnace
Primary or secondary?
Once again, you'll have to determine which is the primary wiring and which is the secondary. If you had a wiring diagram with the wire colors labeled, this is simple. If you don't, you'll have to figure it out.
Wire color
In the US, typically the ungrounded (hot) conductor will be black, and the grounded (neutral) conductor will be white. It's common for this color code to follow through to the primary side of the transformer, so a set of black and white wires is likely the primary side. The secondary could be any color, though commonly the R
wire will be red.
Wire size
You may also be able to determine which is which, based on the size of the wires connected. The primary wires will typically be either 12 AWG or 14 AWG, whereas the secondary may be smaller.
Measure.
If all else fails, pull out your voltage meter an measure. The primary side will be line voltage, and the secondary will be low voltage (commonly around 24V).
Trace the wires
Now that you know which wires are connected to the secondary coil, simply follow them to their termination. One of the wires will be connected to the R
terminal, the other may or may not be connected to a terminal that is labeled. But even if it's not labeled, it's still C
.
Transformer connected to two wire, heat only thermostat.
Transformer connected to three wire, heat only, WiFi thermostat.
For more information on transformers and C
wires, please see More than you've ever wanted to know about the C wire
Best Answer
Since you haven't supplied much detail, I'll have to use nonspecific examples based on typical installation methods.
Furnace and Condensing unit
If you have a setup where you have a furnace, and an outdoor condensing unit. The wiring will be similar to this (Note: This is a basic overview, not actual wiring).
Basically, the
R
wire provides power to the thermostat.W
,Y
andG
are energized depending on the state of the thermostat. For example. If the thermostat is set to theCOOL
mode, and the temperature in the room is above the set point. TheY
andG
terminals of the thermostat will be energized. This tells the furnace to turn on the blower at high speed, and the condensing unit to turn on. Alternatively, if the thermostat is set to theHEAT
mode, and the temperature in the room is below the set point. TheW
terminal will be energized, which tells the furnace to turn on.Heat Pump
If you have a heat pump, the wiring will be similar to this.
Here the
R
wire again provides power to the thermostat. This type of setup uses either anO
,B
, orO/B
terminals to change the state of the reversing valve in the heat pump. In this type of setup, the thermostat works similar to the example above, though it also has to manage an extra terminal.Some thermostats offer both an
O
and aB
terminal.When the thermostat is in
COOL
mode and calls for cool, theO
terminal will be energized. If you have a system where the reversing valve is normally inHEAT
mode, you'll use theO
terminal to move the reversing valve toCOOL
mode. When the thermostat is inHEAT
mode and calls for heat, theB
terminal will be energized. If you have a system where the reversing valve is normally inCOOL
mode, you'll use theB
terminal to move the reversing valve toHEAT
mode.Some thermostats offer and
O/B
terminal, and will have a jumper to select which function it provides.In this case, you'll set the jumper based on the type of system you have. Then when the thermostat calls for heat or cool, the
O/B
terminal will be energized appropriately.For more information on the
C