I installed a furnace evaporator and condenser brand goodman 4 ton unit but need to know how to connect thermostat from condenser to the furnace to the thermostat if any suggestion.
How to connect thermostat to newly-installed condenser/evaporator unit
hvac
Related Topic
- R-410a pressure problem, 285/120 psig
- Change an orifice to make an R22 evaporator unit compatible with a 410a unit
- Why does the new furnace vibrate and smell like burnt oil
- Nest thermostat causing condenser unit contactor to chatter when NOT calling for cooling
- Should the AC condenser and evaporator be the same size
- Is TXV required when an appropriate piston/orifice is used
- What type of bracket to use between furnace and evaporator coil unit
Best Answer
In the condensing unit, locate the contactor. There should be at least two low voltage terminals on the contactor (commonly on the side). Run a two wire cable between the condensing unit, and the furnace. Connect the wires from the cable, to the low voltage terminals on the contactor. In the furnace, connect one of the wires from this cable to the
Y
terminal, and the other to theC
terminal.At the thermostat, connect the yellow wire (or any additional wire in the thermostat cable), to the
Y
terminal. Connect the other end of the yellow wire (the wire you connected to theY
terminal of the thermostat), to theY
terminal of the furnace.Notes: