I would like to replace a regular plug with a GFCI plug. The current plug has:
- Ground (green in picture)
- White
- Black
- Red (connected on the same side than the Black with broken tap)
The breaker is "double" (see picture)
To the best of my knowledge, there is no switch linked to half of the outlet.
Thank you!
Best Answer
Multi Wire Branch Circuit
You have an MWBC. It provides 2x the power with 1.5x the wires (3 wires instead of 4). The catch is:
Your old setup has all of that. What it doesn't have is GFCI protection. While with an ordinary single circuit, you can install GFCI at the point of use (a combination GFCI/receptacle) or in the panel, with an MWBC the usual solution is in the panel. You do actually have an alternative, but it is more work and only makes sense if you also want to have more receptacles:
That will essentially split the MWBC into two separate circuits, each of which can handle a full 15A load. If you want to use two large tools in one place and nothing else, then the existing receptacles (plus GFCI in the panel for safety) makes sense. But having 4 receptacles (2 on each of 2 circuits) can be very useful.