Subpanel Ground Wire – How to Properly Size Ground Wire for Subpanel

subpanel

What is the general rule for sizing ground wire relative to the conductors? I know I saw this somewhere on here, but I cannot find it.

I'm running aluminum (#1 AWG aluminum) to my subpanel and I'd rather not try to tie a #1 wire into my ground bar. Can I use #4 Al for ground?

Best Answer

YES you can use #4 Al as your ground. Your 1AWG Al is good for a 100 AMP feeder (actually 110). From NEC 250.122 this requires an #8 CU or #6 Al ground wire as a minimum (or 6CU and 4 Al if you are really running a 110Amp Feeder).

As a reminder, your feeder will be 4 wires, the two hots and the neutral will be #1AL (unless you've de-rated the neutral to 70% or from specific load balancing calculations if that is allowed in your area).

NEC 250.122 table:enter image description here