I have installed a single toggle switch/outlet on a GFCI circuit and the outlet is fine, however, the toggle switch for 3 recessed led lights trips the GFCI.

It a Remodel. I have run 12/3 w/grd from source to a gfci outlet. In the circuit is a switch/outlet. The red wire is being used for switch loop.

Best Answer

The circuit as you have designed it will not work. You have routed current from the load hot terminal of the GFCI through the switch and load, then back to the neutral node in your service panel, bypassing the load neutral terminal of the GFCI. The GFCI senses this imbalance and trips.

You cannot mix a GFCI protected path with an unprotected path. You must either power the toggle switch and LED load completely from the GFCI load terminals, like this:

protected switch and light

or power the toggle switch and LED load completely from the unprotected mains supply, like this:

unprotected switch and light

One path or another will require a 12/4 w/g instead of a 12/3 w/g cable.