At Thermostat
- Fan was on Auto
- Cooling was On
Outside Unit was making noise.
Outside Unit Fan not coming on at all
Next to the compressor on the Wall there was On Off Switch, I turned off power from the outside unit but it still kept making that noise
https://www.youtube.com/watch?v=CYYfuzDp5DU&feature=share
I went inside turned off the Cooling and noise went away
It has two capacitors
30uf and another small one 5uF
Unit is Lennox
- Is the issue with my capacitors?
- Can i replace these two capacitors with a single 35uf one ?
- Or i am thinking it completely wrong and it's something else?
Best Answer
Sounds like contactor chatter. Could be a bad contactor, or not enough power on the coil.
Basically, the contactor is closing and opening really quickly. This happens when the coil doesn't create a strong enough magnetic field to hold the contactor closed.
Depending on the cost of a new contactor, I'd probably just pop in a new one. If it doesn't fix the problem, you'll have to troubleshoot further. If you have (or can find) the manufacturer's specifications for the contactor, you could measure the contactor coil resistance and compare it to the spec.
You can also check the voltage of the control wiring going to the contactor coil.
You should measure about 24 volts (assuming it's a 24 volt control system).