My old range is on a 60 amp circuit. I'm replacing the range with an oven (40 amp) and cooktop (30 amp).
I currently have a Siemens 60 amp breaker and label states awg 6-4. I want to replace it with a 70 amp breaker where label also states awg 6-4. So is it ok to change the breaker from 60 to 70 without changing the old wire?
Don't know size of wire. But I assume is 6. So if it is 6, do I need to change the wire?
Update: Thank you for everybody's reply. I don't know if this info helps. The cooktop is 8300 watts and the oven is 6325 watts. I currently have a 60 amp breaker. Can I just use the 60 amp breaker and not even changing it to 70 amp? Cause that would be the best option for me.
Best Answer
This isn't just an adding job
Your assumption that your oven & cooktop combination requires a 70A breaker is actually incorrect -- this is due to the 220.55 demand factors in the NEC, as it's pretty implausible that the oven will be going at full broil and all four cooktop elements will be on full blast all day long on other than very rare occasions. (That, and neither of your appliances require a dedicated branch circuit in their installation instructions.)
Applying the logic of table 220.55, note 4:
to our circuit gets us a total unfactored load of 14.625kW. Since this is over 12kW, we must then apply 220.55 note 1 to the 8kW column C value for a single range to get the factored load:
Applying this logic gives us a 15% increase in demand, or 8*1.15 = 9.2kW, which is well within the capacity of a 60A branch circuit! (In fact, you could run this combo off of a 50A branch circuit if you so chose.) Given that the use of 220.55 factoring for range circuit sizing is expressly permitted by the NEC in 422.10(A), paragraph 4:
we can safely say that you don't need to change your breakers here, as the factored load is considered the "maximum load served" for the purposes of 210.19(A)(3).