The cooling test sequence for this board, says to jumper Y
& G
to R
. Make sure the fan comes on, and spins up to the proper speed. Then remove the jumpers, and check the fan off delay.
If the blower does not come on, verify that the COOL terminal is energized. Use a voltmeter between COOL and neutral, and verify 120 volts (with jumpers in place).
If the COOL terminal is energized, check the motor and verify all speeds are working properly.
If the COOL terminal is not energized, the board my be bad.
According to the schematic you've provided, you have a multispeed blower (which is quite common). The speed at which the motor runs, is determined by which wire is energized. Energizing the red wire; for example, will run the motor at low speed. Energizing the black wire, runs the motor at high speed.
Before you disconnected the board, one of the motor wires was connected to the HEAT terminal on the board, and one was connected to the COOL terminal. Looking at the ladder diagram, it looks like the blue (MED) wire was connected to the HEAT terminal, and the black (HI) wire is connected to the COOL terminal.
If you've run the tests described above, and found that the COOL terminal is energized when the jumpers are in place. You can try connecting a different speed wire to the COOL terminal. If the motor spins up with the other wire connected, it means that the original speed is dead or something's wrong between the board and the motor.
It looks like the LO speed red wire is attached to the M1 terminal on the board. I'd swap that to the COOL terminal (just temporarily for the test), and see if the motor spins up when the jumpers are in place.
WARNING: DO NOT run the A/C for long with the motor at a lower speed..
Best Answer
Raising fan speeds during heating season can be counter productive. Shutting vents off does not mean more air will flow as we desire. In most instance power consumption increases. The best option is to increase duct size for a significate portion of the run if the duct was properly sized to begin with. Duct runs should never run over 25 feet remaining the same size. Duct runs generally should be limited to no more than 20 linear feet. A 100 square foot room generally will need a 6" duct.