Is wiring laying alongside an attic access opening a code violation or safety concern

atticfire-hazardsafetystoragewalkway

I have a new house nearing completion in Manning, South Carolina, with all non-metallic jacket wire. However, the scuttle holes for two retractable stairs and attic lift had wires blocking access until I pointed it out, so the electrical sub just pulled the wires drum-tight to the edge of the opening. This means it's always the first thing you step on going up, and likely what someone will snag their foot on for a 15-foot free-fall to the concrete floor on the way down. This includes the primary service to the house with a pair of jacketed 4-4-4 cables for the 400-amp service under your feet in the first step into the attic. The entire attic storage space is completely covered with a massive web of 8-3 and 12-2 wire where subs have slid the walkway and storage area OSB under the wires, meaning that the only place to walk or store anything is on top of the wiring. Because of the size of the larger wires, it becomes a fall hazard if the floor is raised to clear them due to the increased step height of the top step to the attic floor. I just don't see how this could possibly meet any electrical or fire safety code. Nothing in the house was immune to this level of incompetency from the ground, up. Any ideas?

Best Answer

This sounds like an issue from a physical damage standpoint

While the NM cable only needs to be protected by guard strips if it's within 6' of a scuttle hole in your case, as per NEC 320.23(A) (referred to by NEC 334.23):

(A) Cables Run Across the Top of Floor Joists. Where run across the top of floor joists, or within 2.1 m (7 ft) of the floor or floor joists across the face of rafters or studding, the cable shall be protected by guard strips that are at least as high as the cable. Where this space is not accessible by permanent stairs or ladders, protection shall only be required within 1.8 m (6 ft) of the nearest edge of the scuttle hole or attic entrance.

your attic seems to be intended as a storage space. As a result of this, the exposed cabling you describe in your OP would be subject to physical damage, which would require protection from physical damage as per NEC 300.4:

300.4 Protection Against Physical Damage. Where subject to physical damage, conductors, raceways, and cables shall be protected.

and 334.15(B):

(B) Protection from Physical Damage. Cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, Type RTRC marked with the suffix -XW, or other approved means. Where passing through a floor, the cable shall be enclosed in rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, Type RTRC marked with the suffix -XW, or other approved means extending at least 150 mm (6 in.) above the floor.