First, your question
how do I calculate what that new beam has to be given the existing joists and the desired post options?
This is a bit long winded, but it is how we figure it out accurately.
Figure out a design load per square foot (PSF), we typically use 40 PSF live load and 10 PSF dead load for floors and decks. In a simple span, the beam carries the load halfway to the next support or tributary width; in this case 5'. Multiply the PSF x the tributary width to get the pounds per lineal foot (PLF) on the beam, in this case 50 PSF x 5 Ft = 250 PLF. Then, using software or load tables find a beam that can carry that load based on the span of the beam; allowable loads reduce as the span increases. In your case this requires (3) 2x10 DF #2.
I typically use Forte for beam sizing instead of load tables.
For the post sizes, calculate the tributary load which, in simple spans, is the load halfway between supports. In your case, this would be half the beam length between post multiplied by PLF. For your center post that is 250 PLF x 11.5 FT = 2875 LB. Then, using load tables or calculations find a post that can support that load based on height and bracing of the column. Take into account bearing area of the 2x10 at about 625 PSI perpendicular to the grain for a required bearing area of 4.6 Sq. In. In your case a 4x4 is plenty.
Try a column load calculator here
For multiple span beams, cantilevers, and anything outside of "simple span" things are a little different. For this reason I typically use the beam sizing program.
If this is too intense, maybe just be guided by the following.
If I read correctly, you have deck joist spanning about 10' and on one end a single 2x10 "beam" or rim joist that the joist hang into that spans approximately 11'-6" between (3) 4x4 post.
Based on this, your deck joist are structurally OK although maxed out at a 40/10 load, but are deflecting (bending) a good amount giving part of the bouncy feel. You can add 2x6 or larger joist down the middle of the existing joist to firm things up, or just live with a safe bouncy deck.
The 2x10 is definitely undersized and should be addressed. It also contributes to the bounciness. The simplest solution to this is to add (2) intermediate post mid span reducing the span of the 2x10 to below 6'. OR beef up the 2x10 by adding (2) more 2x10's to it nailing 3 16D nails per foot per beam lamination would easily transfer the load between beams.
Finally, the 4x4 post are more than adequate to support a load of 2,875lb. An 8'-0" length of 4x4 can support over 6,000 lb in wet service.
We applied over 10,000lb to a 7' 4x4 in jacking up a floor with no indication of possible buckling; we were compression limited on the member being jacked.
Toenailing into the top of the beam would probably be adequate, if you use slight care until you get the floor fastened to the top of the joists. For a more robust attachement, a 2x6 or even a 1x6 attached to the ends of the joists (nailed into the ends) such that it overlaps the side of the binders with the extra inch will be quite robust. Serves the function of a "rim-joist." Some blocking between the joists at mid-span or third-points would likely be overkill, but is another approach to resist overturning.
I would recommend the above approach.
"hurricane ties" are a metal bracket that may be handier (and may cost less) than the two you mention. They nail to the face of the joist and the face of the binder. But probably overkill for an interior light storage floor. You should be able to install the shortest version of them by simply pushing the insulation down while you nail, and letting it spring back up once installed.
Best Answer
There are two considerations, 1) vertical loads (including uplift), and 2) lateral loads.
1) 2x4’s at 24” o.c. are plenty strong enough to support a roof load of say 30 lbs. per square foot LIVE LOAD (snow load) plus a DEAD LOAD (framing, insulation, etc.) of 10-12 lbs psf for an 18.5” span. However, the connections at each end will be in the 140lbs. Range. So, 2-16d are required (each 16d will support about 80 lbs. each for toe-nailing,) but make sure you don’t split the joists.
If the 2x4’s extend over an exterior top plate, you’ll need to fasten them down by toe-nailing them to be he top plate, (if you don’t want to use clips).
2) Lateral loading (earthquake and high wind resistance) is different. Here you want adequate transfer from roof sheathing to supports. Unless you live on an extreme earthquake zone or high wind area, 2x4 roof supports at 24” o.c. Will be fine.