Non-metallic conduit support on horizontal surface in inaccessible space

conduitnecsupport

NEC says I need to secure 1" nonmetallic rigid conduit (Schedule 40 PVC to be precise) every 3 feet, which makes perfect sense when it is hanging between supports horizontally, across joists, or on a vertical surface.

However, I am looking to run a length of conduit over my porte cochere. The plan is to have it go up into one soffit, cross over attic space (inaccessible, no stairs or opening) feeding it in via the soffit, and come down out the other. Its about 14' across and there is no real way for me to get in there to attach straps. It would lay on 1/2" to 3/4" plywood which constitutes the ceiling of the porte cochere. Can I leave this long of a run without a strap? It is 'supported' by the flooring.

My only concern is its not protected – outside the fact that you would have to drill through the plywood to hit it. There is a run of romex to four recessed lights in this space as well.

If it has to be supported, can I use something like a rooftop pipe support and feed them in to the space?

Any advice or pointing to somewhere in the code that hits this would be very helpful.

Best Answer

You might want to check with the inspector first, but I'm going to say they'll allow it. NEC allows PVC to be supported by passing through framing members, so I'm guessing they'd allow it to be supported where running over framing members (especially in inaccessible areas).

National Electrical Code 2014

Chapter 3 Wiring and Protection

Article 352 Rigid Polyvinyl Chloride Conduit: Type PVC

352.30 Securing and Supporting. PVC conduit shall be installed as a complete system as provided in 300.18 and shall be fastened so that movement from thermal expansion or contraction is permitted. PVC conduit shall be securely fastened and supported in accordance with 352.30(A) and (B).

(B) Supports. ...Horizontal runs of PVC conduit supported by openings through framing members at intervals not exceeding those in Table 352.30 and securely fastened within 900 mm (3 ft) of termination points shall be permitted.