I have a brand new Square D sub-panel installed in my barn that replaced an old panel that had been there for many years and was deemed a fire hazard by the inspector. The new panel has a grounding wire that runs from the panel grounding bar to outside and is connected to a copper rod sunk 6 ft into the ground. For the receptacles on the ground floor I have a 20 AMP GFCI breaker installed in the panel that feeds a single line that they are daisy chained to. The breaker is wired correctly (hot wire to breaker as normal, neutral wire to the breaker neutral and then neutral pig tail from breaker to the neutral bar on the panel. Ground as normal goes to the ground bar on the panel).
When I plug in my outlet tester it reads "Bad Ground" on any receptacle I plug it into in the barn. I tested the same unit in my house and it reads green (all correct). Here's what I've tested so far with my multimeter:
- continuity between receptacle ground pin and ground screw – good
- continuity between receptacle ground pin and ground wire that comes from panel – good
- continuity between ground bar on panel and the other end of the ground wire that connects to the grounding rod – good
What could be going on giving me this reading?
Best Answer
If you only have a three wire feed to the barn then the panel should have the neutral and ground connected together.
The old method of wiring a sub-panel in a separate building was the 3-wire method like you have. The wires should be Hot, Hot, Neutral not Hot, Neutral, Ground.
Consequently the sub-panel would have been bonded (neutral and ground connected together). So, the replacement panel should be bonded.
If you have not bonded the neutral to the ground in your barn that is why your tester is saying it has an open ground.
Here is the pertinant NEC section:
Good luck and stay safe!