Sorry to hear about your "odor" problem. Maybe there is a local public fountain you can take a dip into!!!
However, the problems you describe are fairly common, but may be tricky to isolate. Let's try some basics:
Relieve the pressure from the bladder completely. Let the well pump fill the tank completely and bleed any air from the system using the faucets with the pump running. Again, with the tank full of water, close all outlets and charge up the bladder to about 60PSI. Most systems work fine between 45 to 65 PSI. Anything over 70 is pushing it. The tank needs to be charged when full, not empty.
Monitor the pressure as you draw water. Does the pump kick on constantly when the pressure reaches the low limit, and off at the high limit? This will help tell if the regulator is working properly.
Is there any pulsating water pressure at the faucets?
When you are sure you have a full tank, no air in the system, is your second floor water flow ample when the tank is reading 60psi?
There are a few "if's" here. Depending on how the pump behaves and the pressure responds, you have to determine if the problem is with the pump and volume of water being delivered to the tank, or if the pressure regulator is properly operating.
If you are still seeing any pulsating water pressure at the taps, then the bladder is water logged again. If the bladder pressure drops too quickly, then most likely the volume of water from the pump is low. The pressure should remain fairly constant at the tank if all the functions of the pump and regulator are working properly. Good Luck
First of all the information I'm providing is based on my local codes, your local codes my very.
Quick Answer
You will need to feed the lower floor manifolds with 3/4" PEX inlets and 1/2" outlets. No manifold would be required for the upper bathroom as only 1/2" PEX is needed for both the hot and cold, just tee off the 1/2" lines to feed the sink, tub and water closet. All individual fixture runs would be 1/2" as well.
Detailed Answer
Using manifolds and running to each fixture individually is called a homerun system. This can be less labour but may have a higher material cost. It all depends on how far the groups of fixtures are from the manifold. This method is typically used when the pipes are run through the slab.
Depending on the location of the fixtures, you may want to look at a truck and branch system. This is were you would run two mains and branch off to the fixtures as it passes them. The mains would get smaller as the fixtures are taken off.
Water lines are sized so that the velocity within the pipe is kept below a set point. This is to limit the wear and tear on the pipe material. Different materials can handle different velocities at different temperatures. The max velocity for copper and PVC is 5ft/sec for cold and 4ft/sec for hot. PEX pipe can handle a maximum velocity of 8ft/sec for both hot and cold.
Fixture units (FU) are given to typical fixtures. A FU is a design factor that is used to represent the typical requirement of a particular fixture (it is not a flow rate but).
Fixture Units for Private Use Fixtures (no flush valves):
|--------------------------------------------------------|
| Fixture | Hot FU | Cold FU | Combined |
|--------------------------------------------------------|
| Bathroom Group | 4.50 | 4.50 | 6.00 |
| Bathtub/Shower | 1.50 | 1.50 | 2.00 |
| Clothes Washer | 2.25 | 2.25 | 3.00 |
| Dishwasher | 3.00 | - | 3.00 |
| Hose Bib | - | 7.00 | 7.00 |
| Kitchen Sink | 2.00 | 1.50 | 1.50 |
| Water Closet | - | 3.00 | 3.00 |
| Lavatory | 0.75 | 0.75 | 1.00 |
|--------------------------------------------------------|
The above table lists the common residential fixtures and their FU. You can see that a bathroom can be considered one group and has a lower FU then the sum of it's parts. This is because they are typically used by one person at a time so it is unlikely that all fixtures will be running at the same time.
Once we have the FUs, we can look up a sizing chart that will tell us the maximum FUs that a pipe of a set size and material can handle while staying below the maximum velocity. You can view these tables in the Domestic Water Sizing Tables (For Small Buildings) section below.
Based on this information, we can size your distribution system as follows for PEX:
|----------------------------------------------------|
| Fixture Group | Hot | Cold |
| | FU Size | FU Size |
|----------------------------------------------------|
| Upstairs Bathroom | 4.50 1/2 | 4.50 1/2 |
| Downstairs Bathroom | 4.50 1/2 | 4.50 1/2 |
| Kitchen | 4.50 1/2 | 1.50 1/2 |
| Half Bathroom | 0.75 1/2 | 3.75 1/2 |
|----------------------------------------------------|
So you can see that the pipes feeding each group of your fixtures will only need to be 1/2". Each individual fixture would also be 1/2". However, depending on how the groups of fixtures are located relative to each other, you may require 3/4" pipes to feed more then one group. The total FU of your house is 14.25 Hot FU (3/4"), 21.25 Cold FU (1") and 28.00 Combined FU (1"). The Combined FU is used to size the section of pipping from the cold line into the house to the hot water tank. Don't be alarmed that the cold and combined are sized at 1". This is due to the allowance of the hose bib, which our code now calls for 7 FU. This is too high and has been causing issues in large buildings with hose bibs on small decks, in that the lines are oversized and do not properly flow, allowing for growth in the water. Without the hose bib, your cold is only 3/4".
Domestic Water Sizing Tables (For Small Buildings)
- Minimum pressure available - 60 PSI at property line. (Greater
acceptable).
- Pressure reducing valve set at 60 PSI minimum.
- Pressure loss for meter (3 PSI), maximum building height 25 ft. (10.82 PSI)
- Minimum 0.115 PSI for friction loss. If less than 0.115 PSI, system
must bp fully engineered by detailed method or there will not be
sufficient water to supply the fixture.
Pipe Flow Velocity Table For: Copper & PVC:
|---------------------------------------------|
| Pipe Size | 5ft/sec (cold) | 4ft/sec (hot) |
| | GPM FU | GPM FU |
|---------------------------------------------|
| 4" | 186.65 850 | 149.32 600 |
| 3" | 106.16 400 | 84.93 295 |
| 2-1/2" | 74.37 245 | 59.50 170 |
| 2" | 48.23 120 | 38.58 81 |
| 1-1/2" | 27.72 46 | 22.18 34 |
| 1-1/4" | 19.59 29 | 15.67 22 |
| 1" | 12.86 18 | 10.29 14 |
| 3/4" | 7.54 9 | 6.03 7.5 |
| 1/2" | 3.64 3.5 | 2.91 2.5 |
|---------------------------------------------|
Pipe Flow Velocity Table For: PEX, PE, PB, CPVC & Ductile Iron:
|-----------------------------------|
| Pipe Size | 8ft/sec (cold & hot) |
| | GPM FU |
|-----------------------------------|
| 4" | 300 1800 |
| 3" | 170 750 |
| 2-1/2" | 152 500 |
| 2" | 78 265 |
| 1-1/2" | 44 102 |
| 1-1/4" | 30 54 |
| 1" | 20 30 |
| 3/4" | 12 17 |
| 1/2" | 5.8 7 |
|-----------------------------------|
Best Answer
It truly will not be as efficient as 2 separate lines feeding each fixture, or 3 separate lines for 3 fixtures.... You will only notice a pressure drop when both fixtures on the same branch are used at the same time. You will see the difference, it may not be drastic enough to need to gut what ever is in the way to get it run everywhere. If I remember right, Maniblock only has 1/2" connectors?