gfci

I am changing out another regular outlet to a GFCI outlet and the existing outlet had the four wire connection using all the terminals. It is an older condo and there are no grounds. So I thought I would wire the four (two white and two black) the exact way on the new GFCI. The green light is on but no power in the new GFCI outlet and I cannot push the "test" button. I have seen mixed responses to similar questions, so I wanted to pose my exact situation. It is a new Leviton 15A GFCI and based on some other responses to other questions it sounds like I should try to switch the connections (reversing them top to bottom), which I will try when I get back down there, but I am not replacing another GFCI outlet and if the regular outlet replaced has the metal connections intact between the side terminals, I would not think that should matter, but perhaps it does. Any thoughts or confirmations would be appreciated, I wanted to ask before I swap the wires around (not hot for neutral, but line for load).

Best Answer

Regular receptacles have screws for splits (one switched, one always on or two switched but different circuits or two on separate circuits for higher total power) & for convenience (the way you and most people use them). GFCIs can't do splits and use them for convenience to connect another receptacle only by properly identifying and using LINE vs. LOAD.

Two ways to do this:

Line Only

This is by far the simplest. Pigtail the two blacks together with a short piece of black wire and connect it to the hot screw on the LINE side of the GFCI. Pigtail the two whites together and connect to the neutral screw on the LINE side of the GFCI. Nothing goes on the LOAD side. The new receptacle is protected. No other receptacles on the circuit are protected by this GFCI.

Line and Load

You need to identify which hot & neutral goes back to the panel and which goes on to another receptacle. There are a number of ways to do that - simplest typically is to disconnect all 4 wires, turn the breaker on and see which wires cause a non-contact tester to light up. Connect the "panel" (may be other receptacles in between, and that's OK) wires to the LINE side and the other wires to the LOAD side. Now the new receptacle and everything following it via the LOAD side is protected.

Note that the second method is generally OK and provides additional protection. However, if any of the LOAD side receptacles are things you don't want on a GFCI - e.g., anything like a refrigerator that would have problems if there were a trip of the GFCI and you didn't know about it for a while - then go with the first method.