Replacing a doorbell transformer attached to power extension bar

doorbelltransformer

My doorbell transformer (picture attached) is determined to be dead because the output voltage is zero, while power socket voltage from the junction box is about 122. Thus, the doorbell transformer needs to be replaced or the wiring to the doorbell transformer needs to be taken care of.

Doorbell transformer attached to a junction box with power sockets

Inside of junction box (after shutting down the power, of course) is shown below:

Inside of junction box

As we can see, the wires to the doorbell transformer are connected to the power socket panel. The connection is so firm that I can't pull the wires out. Is there any trick to disconnect the wires from the power panel so that I can replace the doorbell transformer? Or should I just replace the junction box and the doorbell transformer as a whole device?

Thanks in advance.

Best Answer

Do not replace the junction box. It is a standard junction box and there is nothing wrong with it.

Backstab connections fail more often than transformers

Look at the receptacle. See how the wires are connected? They're "back wired" with a backstab style connection. That is only allowed for 14 AWG solid wire, the receptacle's labeling plainly says

PUSH IN #14 CU SOLID WIRE FOR 15A BRANCH CIRCUIT ONLY.

CU = copper. It is then repeated in French.

Looking at the transformer's ground wire it definitely stranded wire that has been tinned with solder to keep it from getting a case of the frizzies. The ground wire has been horked onto the already-occupied ground screw in an impressive display of bad workmanship.

Equally bad workmanship is obvious in the attaching of the transformer wires to backstabs. The wires are stranded and certainly not 14 AWG. This is a violation of NEC 110.3 which requires the instructions and labeling of the receptacle be followed (14 AWG solid only).

Since backstabs have a spectacular failure rate (open circuit) even when they are used to spec, we should expect this to be a failed backstab.

So, I would remove the transformer wires from the backstab (if it's possible to do this while also facepalming), and move each wire to the appropriate screw terminal. I would also pause to inspect the wire for any arcing or galling, because that would explain the mystery.

As far as actually removing the wires, there should be a little slot into which you can jab a tiny screwdriver, and sort of pry away from the wire and that should reduce the extraction force somewhat. Otherwise feel free to just use an excessive amount of force. Worst case the wire will break off inside the backstab and you'll have to strip off another 1/4" to attach it to the screw.

When removing #14 wires, just twist the receptacle back and forth about 60 degrees repeatedly while using serious force. Don't cut; wire length is precious in most cases.

While you're at it, fix the ground

The ground installation was acceptable until this transformer came along. Now it is one too many wires on that ground screw. Move the "U" loop on the receptacle screw so you have about 2" of extra length sticking out (instead of the 1/2" now sticking out). Wire-nut the transformer ground wire to that.