Can I run 3/0 copper se cable wire with the ground to a sub panel straight from the 200 amp breaker box to the 100 amp box through a crawl space without any conduit?

Best Answer

From the 2011 NEC 310.15(B)(7) table. A 100 amp residential panel only requires #4 copper or #2 aluminum. 3/0 copper would be a waste of money.

If you use SE cable you will need 3 insulated conductors along with the bare wire.

338.10(B)(2) Use of Uninsulated Conductor. Type SE service-entrance cable shall be permitted for use where the insulated conductors are used for circuit wiring and the uninsulated conductor is used only for equipment grounding purposes.

Since you a using it for a feeder to a sub-panel you have to have an insulated neutral and use the bare for the equipment ground.

Do not bond the neutral and ground in the sub-panel and keep the neutrals and grounds separated. You need a panel that is "suitable for use as service equipment" since it will have an insulated neutral bar. Discard the green bonding screw.