I'm installing a manual transfer switch to feed a 240V subpanel from either generator or the main panel. No devices other than the main panel are bonded. Since the neutral is not switched, can I bypass the transfer switch with the neutral and ground wires and connect the neutrals from the main panel and the generator directly to the subpanel?

Does the pictured wiring meet code?

proposed wiring

Best Answer

2014 NEC 300.20 (A) "Where conductors carrying alternating current are installed in ferrous metal enclosures or ferrous metal raceways they shall be arranged so as to avoid heating the surrounding ferrous metal by induction. To accomplish this, all phase conductors and where used the grounded conductor and all equipment grounding conductors shall be grouped together". Also see 2014 NEC article 702.