Switch – Does a light circuit in a garage need GFCI protection

ceilinggaragegfcireceptacleswitch

We are in the process of building a new garage. I am putting 4 rows of light on separate light switches, they will be on separate circuits so if a breaker would trip I won't be in the dark.

From what I have read since the lights are plug in they need to be GFCI protected. I was going to come off the panel box to the switch then to an outlet in the ceiling. But once again from what I was reading a GFCI outlet is not allowed in the ceiling.

So my question is does the light switch also need to be after the GFCI outlet or can it be before the GFCI outlet where the light are plugged in?

Also can the GFCI outlet be at the top of the wall just not on the ceiling or can it only be so high off the floor? I don't really want to have 4 outlets right beside my switches.

Best Answer

The requirements for GFCI protection are in NEC 210.8(a):

210.8 Ground-Fault Circuit-Interrupter Protection for Personnel. Ground-fault circuit-interrupter protection for personnel shall be provided as required in 210.8(A) through (E). The ground-fault circuit interrupter shall be installed in a readily accessible location.

and (A) tells you that receptacles in garages require GFCI protection.

The NEC has a very specific definition for readily accessible and if you need a ladder to get to the receptacle, it's not readily accessible.

Your cord and plug lights plug into receptacles, which require GFCI protection with the test-reset buttons in a readily accesible location. That does not mean that each receptacle in the garage must be GFCI type; if they are on the LOAD side of a GFCI breaker, receptacle, or dead front, they're protected. The dead front or first receptacle could go in any readily accessible location - by your switches, next to the panel, where ever you want.

GFCI breakers are a pretty straightforward way to handle it, if you've already started wiring this would fix your issues easily.

Dead fronts next to the switches would be nice, that's a nice conspicuous spot - easy to notice the indicator light when they trip. You could install a second box right above the switches. The circuit would come from the panel to the dead front then to the lighting.

Receptacles might be the way to go. The wiring would go to the LINE side of the GFCI receptacle then the rest of the receptacles - on the wall or in the ceiling - would be fed from the LOAD terminals on that first GFCI receptacle. This is probably the way to go for what you want.

Unless your garage is warehouse sized, four circuits for lights - probably LED - seems a bit much. Since LED lighting doesn't draw much power, you could put your regular general use wall receptacles on the same circuits as your lights. Maybe hedge and use 20A circuits with 15A receptacles.

Even then, four circuits seems a bit much for most garages. I might put half your receptacles and the odd rows of lights on one circuit, and the other half of the receptacles and the even rows of lights on the other circuit. Hit the GFCI receptacles first in each string and continue on to the rest.