The maximum span for a beam made of two 2x10s screwed together

beamdeck

This is for a deck. If I make a beam out of two 2x10s, what would the maximum span be? The beams will be 8 feet apart (joist span). They will be resting on posts. The number of posts depends on how far the beams can span. This will be standard pressure treated lumber. I was going to use screws to hold the beams together. Maybe construction adhesive, too.

I have a book that says 8 feet, but want to double check that I'm reading the tables right. this is under a deck, no crazy loads like a hot tub.

Thanks!

Best Answer

The Code requires a Live Load of 40 lbs. per square foot (psf) plus a Dead Load of 10 psf for a total load of 50 psf.

You indicate the beams are 8’ on center, so the total load on each beam is: 50 psf x 8’ (4’ on ea.side of beam) = 400 plf

In addition, the code requires an adjustment for wood being pressure treated. If wood is pressure treated without incising then it’s a 5% reduction. If it is incised, then it’s a 20% reduction.

Summary: Depending on the species and grade, 2-2x10’s can span 12’ with pressure treated lumber without incising and 10’-6” with incising. (I’m using a species of SPF and a Grade of No.1)

Note: If the beam is along the edge of a deck and is loaded with a single span, then 2-2x10’s can span about 15’ without incising and 11’ with incising.