I found the "Why doesn't the “fan on” mode work after I installed a new thermostat?" thread on this site and am wondering if the manual rewire steps would also work for a two wire system. The setup: older house with Trane XV80 furnace, two wire setup, thermostat/Rh to controller board/R; thermostat/W to controller board/W1; thermostat Rc to Rh jumper; controller board W1 to W2 jumper. As I understand it an additional green wire would be the best solution, but that's not an option for me. Can I get the fan to run continuously during the summer by manually moving the thermostat wire from Rh to G and the controller board end from W1 to G? Thanks.
Trane XV80 furnace, two wire setup, wanting continuous fan when no heat is needed
furnace
Best Answer
It's probably simpler to just wire a switch at the furnace wired R and G. In the summer you just hit the switch. You can switch the wires in your furnace and thermostat to have control at the stat. Or you could install a Fast Stat, which uses two wires to signal a full complement of wires.