If you're not planning on installing an electrical panel in the garage, the installation is quite straight forward. You can basically treat the garage circuit, just like any other branch circuit. If you do plan on installing a panel in the garage, the following information is not for you.
Overview
You'll install a 20 ampere breaker, in the panel in the house. From there you can either go straight into conduit, or you can run any other approved cable. From the question, it sounds like you want to use nonmetallic sheathed cable from the panel, which is just fine. You'll connect the 12/2 with ground NM cable appropriately in the panel, and run it out to a junction box near where the conduit will leave the house.
Then you'll run conduit from that junction box, outside, underground, then up and into the garage, ending at another junction box. You'll want to make sure you install expansion fittings where appropriate, especially if you're entering the buildings above ground.
Next you'll pull three, 12 AWG THWN wires through the conduit. Connect the wires from the NM cable, to the THWN conductors in the junction box in the house.
Finally, you'll run cable from the junction box to the outlets in the garage.
Single, or Multi-wire branch circuit
National Electrical Code allows a garage to be supplied by a single, or multi-wire branch circuit without much trouble. If you don't plan on using much power, and don't mind having the lights and receptacles on the same circuit. You can simply run a single circuit out to the garage, and power everything with it. However, if you want to separate the lighting load from the receptacles load, you can install a multi-wire branch circuit without much extra effort.
If you decide to install a multi-wire branch circuit, you'll have to install a double pole breaker instead of a single pole breaker. So to do this, you'll have to have two slots open in the panel. You'll also have to install an additional conductor, so you'll have to use 12/3 NM cable and pull and extra wire through the conduit.
Conduit Size
Whether you decide to install a single or multi-wire branch circuit, you'll need to use at least 1/2" conduit if you're using schedule 80 PVC. According to Table 5 of Chapter 9 of the National Electrical Code, each 12 AWG THWN conductor has an approximate area of 0.0133 in.². Table 4 of the same chapter, says that 1/2" schedule 80 PVC has a total internal area of 0.217 in.². However, since there are more than 2 wires in the conduit, you can only fill the conduit to 40%.
0.0133 in.² * 3 conductors = 0.0399 in.²
0.217 in.² * 0.40 = 0.0868 in.²
Three 12 AWG THWN conductors will take up 0.0399 in.², while 40% of the total internal area of 1/2" schedule 80 PVC is 0.0868 in.². So there's no problem fitting the 3 conductors through the conduit.
0.0133 in.² * 4 conductors = 0.0532 in.²
Even if you decide to run a multi-wire branch circuit, you'll still have plenty of room in the 1/2" conduit.
Conduit Minimum Cover
According to Table 300.5 of the National Electrical Code, direct burial nonmetallic raceways not encased in concrete or other raceways is required to have a minimum cover of 18" (450 mm). However, if it's a residential branch circuit, 120 volts or less, GFCI protected, with 20 ampere or less overcurrent protection, it can have a minimum cover of 12".
So if you're installing a single branch circuit to supply the garage, you can install a GFCI breaker and you'll only have to bury the conduit 12". Otherwise, you're going to have to bury the conduit 18".
NOTE: Minimum cover is based on the conduit running under nothing but grass and dirt. Minimum cover may vary if run under concrete, walkways, streets, parking lots, etc.
Grounding and Bonding
Since you'll only be installing a single or multi-wire branch circuit, you'll only be required to run an appropriately sized grounding conductor along with the current carrying conductors (250.32(A)Ex. 1). You'll extend this grounding conductor to each outlet, and connect any devices to it. There are no other grounding or bonding requirements, as long as there are no metallic pathways connecting the two structures.
Means of disconnect
As Speedy Petey points out, you'll also need a means of disconnect inside or outside the building near where the circuit enters (225.31, 225.32). A means of disconnect is simply any approved method of disconnecting all ungrounded conductors. This could be simple snap switches, a pullout disconnect, a safety switch, etc.
Outlets required
Once you supply a garage with electric power, you'll also have to install a few required outlets. First you'll need at least one receptacle outlet (210.52(G)(1)), which will have to be GFCI protected (210.8(A)(2)). You'll also have to install one switch controlled lighting outlet inside (210.70(A)(2)(a)), and one switch controlled lighting outlet on the outside to provide lighting for the entrance/exits (210.70(A)(2)(b)).
Single branch circuit supplying garage
Multi-wire branch circuit supplying garage
Notes:
- This answer is based on National Electrical Code 2014, and may not be applicable to areas that do not follow NEC.
Base Conductor Size
Start out by using Table 310.15(B)(16), and applying any required corrections, to determine what size conductors you'll need. For your situation, we'll assume we can use the 75°C column, that you want to use copper conductors, and there's no other corrections required. So in your case, if you want to install a 50 ampere panel, you'll need at least 8 AWG copper conductors. If you want a 60 ampere panel, you'll need 6 AWG copper conductors.
Voltage Drop
Once you have the base conductor size selected, you'll want to calculate the voltage drop across that size conductors for the length of the feeders. The first step here will be to use Table 8 from chapter 9 of the NEC, to determine the resistance of the conductors you've selected.
In your case, 8 AWG stranded copper wire has a resistance of 0.778 ohms per 1000 ft. 6 AWG stranded copper wire has a resistance of 0.491 ohms per 1000 ft.
Next you'll use the following formula, to calculate the voltage drop across the feeders.
V = L * 2 * R * A
Where:
- V = Voltage Drop
- L = Distance along the wire from one breaker to the next.
- R = Resistance per foot of wire.
- A = Current running through the conductor.
For a 50 ampere circuit, 130 ft. long, using 8 AWG stranded copper conductors, the calculation looks like this...
V = 130' * 2 * 0.000778 * 50 A
V = 260 * 0.000778 * 50 A
V = 0.20228 * 50 A
V = 10.114 V
10.114 V is 4.2% of 240 V. The NEC recommends having a voltage drop less than 3%. To achieve this, you're going to have to use larger conductors.
6 AWG stranded copper conductors have a resistance of 0.000491 ohms per foot, which means the voltage drop would only be 6.383 volts or 2.7%.
For a 60 ampere circuit 130' long, 6 AWG stranded copper conductors would have a voltage drop of 7.6596 volts or 3.2%. While 4 AWG stranded copper would be 4.8048 volts, or 2%.
Conductor Type
Once you know what size conductors you need, you'll have to determine what type of insulation the conductors should have. Since you're burying the conduit, you'll need a wire rated for wet locations. The popular choice in this situation, would be to use THWN wires.
Wire Size
Now that you know what size conductors, and what type of wires you'll use. Then next step is to determine the physical size of the wires, and how much space they'll take up in conduit. For this, you can use Table 5 from chapter 9 of the NEC. There you'll find that 6 AWG THWN wires have an area of 0.0507 square inches, while 4 AWG THWN wires have and area of 0.0824 square inches.
Conduit Fill
Using the size of one wire, you can figure out the area required for all four wires.
0.0507 * 4 = 0.2028 in.sq.
0.0824 * 4 = 0.3296 in.sq.
Use Table 1 from chapter 9 of the NEC, to determine the allowable conduit fill percent. Since you'll have more than 2 conductors, you can fill the conduit to 40%.
Conduit Type
If you know what type of conduit you're using, you can use Table 4 from chapter 9 of the NEC to look up the area fill values for various sizes of conduit.
Conduit Size
Since you've decided to use Schedule 80 PVC, you'll simply find that table in Table 4. Then look down the 40% fill column, until you find an area large enough for all your wires.
In your case four 6 AWG THWN conductors, will require 1" Schedule 80 PVC. While four 4 AWG THWN conductors, will require 1 1/4" Schedule 80 PVC.
Conduit Size Alt.
If you don't feel like calculating wire/conduit area, and all the wires are the same size, you could use Table C.9 from Annex C of the NEC to look up the conduit size required. There you'll find that you can fit five 6 AWG THWN wires throug 1" Schedule 80 PVC, and that you can fit six 4 AWG THWN wires though 1 1/4" Schedule 80 PVC.
tl;dr
- For 130' long 50 ampere feeder, use four 6 AWG stranded copper THWN conductors though 1" Schedule 80 PVC.
- For 130' long 60 ampere feeder, use four 4 AWG stranded copper THWN conductors through 1 1/4" Schedule 80 PVC.
NOTES:
- This answer contains some of the tables used in this answer.
- If you don't feel like doing any maths, you can surely find a calculator online to do all the work for you.
Best Answer
Pull the cable (USE-2 in conduit? - that was masochistic) back (or out, but back is adequate), cut the conduit, make it go where it should, send the bill to the contractor, pull the cable forward again. You do have to attach a pulling rope to the cable end and not cut that in the process, unless you do pull it all the way out.
Edit: following the last bit of comment (as of this edit) you could dig down to place a hand-hole over the conduit coming up 18" from the building, and (not strictly code compliant, but...) carefully cut the conduit away from the wire just above the bottom of the hand-hole (or more easily, just above where the bottom of the hand-hole will be, when you install it) and install a second, separate run of conduit the short distance from the hand-hole to the side of the building. So if you buy a 12" deep hand-hole, cut the conduit 9" below ground level, install the hand-hole flush with ground level, and either make waterproof splices (to new stranded wires) or pull the uncooperative USE cable the short distance to the building if there's adequate cable to do that. Submit the bill for the hand-hole and new conduit to your concrete contractor.