URD 1/0 wire for 100amp subpanel 60′ away from main box

subpanel

Can I use URD aluminum 1/0, 1/0, 1/0, 4 wire to run a 100 amp subpanel approx. 60' away from my main box? I plan I running it through my attic which in Arizona can get very hot in summer time if there are temperature concerns with this type of wire.
Thanks!

Here's the wire:
https://www.amazon.com/dp/B0748B57B3/?coliid=I1882CE450GCTE&colid=1CFF7GENXIV3T&psc=1&ref_=lv_ov_lig_dp_it

Best Answer

Here is the UL standard summary for that type of cable:

https://standardscatalog.ul.com/standards/en/standard_854_12

It says:

1.2 These cables have insulation of solid, extruded dielectric material(s) that are for use in wet locations at 75°C (167°F) and lower temperatures. Cables that are marked with a conductor type that includes the letters "HH" have insulation that is for use in dry locations at temperatures as high as 90°C (194°F) as well as in wet locations at 75°C (167°F) and lower temperatures. Cables that are marked with a conductor type that includes "-2" have insulation that is for use in wet or dry locations at temperatures as high as 90°C (194°F).

So unless you attic is getting above 90C (which is REALLY hot!) you should be good.

Are you sure you need 1/0 here? That's a huge gauge for 100A. But yes, that will work.