Walls – Wall outlet trips circuit breaker

receptaclewalls

enter image description here

This is a normal 15A 125V wall outlet in my dining room. It consists of 2 black hot wires, 2 white neutral wires, and a bare copper ground wire. Here is the problem. If I wire all 4 wires to the 4 side screws on the receptacle, the circuit breaker for this section trips. If I just wire one hot and one neutral to either the top or bottom, there is no problem. The ground wire is always connected. What is the problem here and how can i fix it? Thanks.

Best Answer

There are three typical reasons to have two black/white/ground cables going into an ordinary duplex receptacle:

1 - Separate circuit for top and bottom to get more power - i.e., 15A on each outlet instead of 15A for the pair together. In this situation the receptacle would have the tabs broken off, cables supplying power coming from two different circuits, possibly sharing a neutral as a multi-wire branch circuit (MWBC) or possibly just two entirely separate circuits. Connecting both cables to a new outlet with the tabs in place would trip the breaker as described. However, the pictures you posted of the old receptacle clearly shows the tab (at least one side) intact.

2 - One outlet on a switch and one "always on". This is often done to have a light plugged in and controlled with a switch while still having some power always on for other devices. In this case typically, but not always, the power would all come from one circuit. The tabs would be broken off. The result, if you connected a new duplex outlet without breaking off the tabs would typically be that both outlets would be always on and the switch would be ineffective - but the breaker would not trip. There is also a possibility that a switch loop could be messed up here, causing part of the problem.

3 - One cable "in" and one cable "out". This is very common. You have a chain of receptacles, each with two cables, except for the last one. If that's the case, the preferred method (as I have learned recently) is to pigtail and only use one pair of screws on the receptacle, but using both one set of screws for each cable, with the tabs in place, would work just fine. But that would not explain the breaker tripping, and you would also have other receptacles or lights or something not working any more.

Take a look at the old outlet and the new outlet. The new outlet has a connection tab on each side between each pair of screws. If the same tab on the old outlet was broken off then the old outlet was fed either by two separate circuits or one receptacle was switched. If that is the case then you can either use one set of wires and cap (wire nut) off the other set of wires, or you can break off the tabs from the new outlet and wire one pair to the top and one to the bottom.

However, if this is the situation then:

  • If there were two circuits then you should have TWO breakers that need to be turned off to get both circuits turned off, not one. If you really only needed to turn one off then there is something else going on. If you really needed to turn off two breakers and didn't realize it, then you are very lucky.

  • The wires should be in clear pairs. (I believe you have confirmed that with the later pictures). If it is not 100% clear which white goes with which black then STOP. If the two circuits are a multi-wire branch circuit then the neutrals are shared and it doesn't matter. But if they are two totally separate circuits then this matters a lot as the neutral and hot have to match.

After all of that, I am a bit baffled. A tester to check voltage would really be helpful here. There could be hot/neutral swapped somewhere along the line (dangerous, but would explain the problem) or something else.

Also, as Harper noted, the backstabs are a very bad thing. I don't think they are the problem here (except perhaps why the original outlet went bad) but they are frequently a source of problems. But with my understanding of the nature of the backstab problems, that wouldn't explain the problem you are having with the two cables tripping. In any case, do NOT use backstabs on any new receptacles, and if you disconnect any backstab wires, reconnect them only to the screw terminals.

The key thing now is to figure out whether both cables are hot or not. If they are both hot then you should only be using one with tabs in place. If only one is hot then you need to figure out where the other one goes to check for problems at the other end.