Water – Code for elevating water heater in garages

code-compliancegaragehot-waterwater-heater

A gas/propane water heater in a garage is elevated. This is to ensure the open flame (at the bottom) is above a certain height (?) to avoid any combustible fuels in the garage from igniting.

This all makes sense.

But does it apply to electric/heat pump hot water heaters? I assume not, as there is no flame to cause combustion, but I'm not sure where in the code to find out if this is true or not. Is it a plumbing code? Electrical?

Best Answer

As I suspected, the code you're referencing is from the National Fuel Gas Code. I was not able to find anything in National Electrical Code, or International Residential Code that mentions this in the context of electric appliances.

So this code only applies to gas water heaters, and only those that are not listed as flammable vapor ignition resistant (FVIR).

NFPA 54: National Fuel Gas Code 2015

Chapter 9 Appliance, Equipment, and Accessory Installation

9.1 General.

9.1.10 Installation in Residential Garages.

9.1.10.1 Appliances in residential garages and in adjacent spaces that open to the garage and are not part of the living space of a dwelling unit shall be installed so that all burners and burner ignition devices are located not less than 18 in. (460 mm) above the floor unless listed as flammable vapor ignition resistant.