Our old circuit breaker for our water heater seems to be at the end of its life. However, the breaker also controls our well system, and the breaker is only 20 amps. Is it okay for us to just replace the breaker (the old one lasted a good 15-20 years) or should we consider having an electrician separate out the well onto a new circuit? There is an open slot in the circuit box if needed.
Water – Should I replace an old breaker or add a new one
circuit breakerwater-heater
Related Topic
- Electrical – How to figure out what this 30amp 2 pole breaker is doing
- Water – Is it safe to keep using this 30amp safety breaker for water heater
- Electrical – Tandem breaker needs both thrown to break circuit. Incorrectly wired
- Electrical – AFCI Breaker Randomly Tripping – No New Devices
- Electrical – Should I make space for a new 50A breaker in a full panel or install a sub-panel
- Electrical – use a 15A breaker for a 10A baseboard heater
- Electrical – Is it ok to run a 30A water heater circuit on #12 wire
Best Answer
I would definitely have the two circuit separated. In fact, they should have been from the start.
If the water heater is a "standard" 4500 watt tank-type then a 20A breaker is not adequate anyway. You'd need #10 wire with a 30A two-pole breaker.