Weather Resistant Outlets vs Weather Proof Box

gfciweather-resistant

If I use a regular GFCI in a Weather Proof In-Use box does the GFCI have to be the Weather Resistant kind?

Best Answer

Yes. If the receptacle is in a wet or damp location, the receptacle must be a weather-resistant type.

In a damp location, you can use any weatherproof cover. In a wet location, you must use an "extra-duty" cover. "Extra-duty" covers, provide weatherproofing even when a cord is attached to the receptacle.

National Electrical Code 2014

Chapter 4 Equipment for General Use.

Article 406 Receptacles, cord connectors, and attachment Plugs.

406.9 Receptacles in Damp or Wet Locations.

(A) Damp Locations ...All 15- and 20- ampere, 125- and 250-volt nonlocking receptacles shall be a listed weather-resistant type.

(B) Wet Locations.

(1) 15-and 20-Ampere Receptacles in a Wet Location. ...All 15- and 20 ampere, 125- and 250-volt nonlocking-type receptacles shall be listed weather-resistant type.

Chapter 1 General

Article 100 Definitions

Location, Damp. Locations protected from weather and not subject to saturation with water or other liquids but subject to moderate degrees of moisture.

Location, Dry. A location not normally subject to dampness or wetness. A location classified as dry may be temporarily subject to dampness or wetness, as in the case of a building under construction.