What should the main panel breaker size be to control a 60amp GFCI for a hot tub and a 15amp GFCI outlet. The gfci's are mounted in a box that will be wired to the main panel.
What breaker size for box containing two GFCI circuits
circuit breakergfci
Related Topic
- Electrical – It it safe to have a 15 amp GFCI outlet on a 50 amp GFCI breaker
- Electrical – Replacing GFCI outlet inside 2-gang box
- Electrical – two circuits on a single pole GFCI breaker
- Wiring – Double-pole, 240-Volt, 15 Amp GFCI circuit breaker to create two 15amp 120 circuits for switched split receptacles
- Electrical – My house breaker box have only breakers which seat only 1 wire. No seat for a load neutral. Can I still install a GFCI Breaker
- Electrical – 100 A GFCI breaker feeding a sub panel main lug
- Electrical – Two hots, one shared neutral, can it work with plug on neutral GFCI/AFCI breakers
Best Answer
The breaker feeding the sub-panel must be sized not exceed the rating of the sub-panel. So, if you install a 60 amp sub panel you can't protect it (fuse it) any higher than 60 amps. Ditto for 100 amps.
The conductors should be sized large enough to carry the load of the sub-panel and be protected by whatever breaker they are attached to.