I had a thermostat get hot and smell, replaced thermostat. Still not working found fuse on control board blown replaced fuse. Lights on control board indicate no problems. Replaced 18/5 cable from control board to thermostat. Still not working. Replaced cable from control board to condenser. Was able to manually start compressor and fan on condensing unit. But still not turning on. Did jumper tests from R thermostat lead and fan and R to A/C wire on control board, both caused 3amp fuse to blow on control board. Replaced 24v transformer was getting high voltage. Still not working. I don't know what to try next, I would think a control board but the heat works and the lights say it is operating fine. This is a Lenox brand system.
What could be causing the A/C not to come on
hvac
Best Answer
If the system run normally when the thermostat is calling for heat, and when the fan control is switched to the
ON
position. Then the first thing I'd look at, is the contactor in the condensing unit.WARNING: If you're not comfortable opening the condensing unit, and/or working with electrical devices. PLEASE contact a licensed and insured HVAC technician.
Locate the contactor.
Using a multimeter set to measure resistance, measure the resistance across the coil.
Typically the coil should measure between 9-12 ohms, though this may vary by manufacturer. You may want to contact the condensing unit dealer, or the contactor manufacturer for model specific values.
High resistance
If the value is higher than 12 ohms, it's likely that the coil will not be able to pull the contactor closed. Which means the condensing unit will never turn on.
Infinite resistance
If there's infinite resistance across the coil, the coil is completely broken. Again, this will never pull the contactor closed.
Low resistance
If a low resistance is measured, it's likely there's a short in the coil. This will typically result in burnt out transformers, and/or blown fuses.