The new thermostat I purchased doesn't run on batteries, and needs 24 volt power. I have only a red and a white wire connected between the boiler and the thermostat, but there is also a third, unused wire. The instructions from the thermostat say to hook that third wire to the C terminal on thermostat and to the furnace's C, but I have a boiler with no C. Where do I put it on here? Please help I'm desperate.
Where’s the C terminal on the boiler control
boilerfurnacethermostat-c-wirewire
Related Topic
- How many wires can be connected to the C terminal at the furnace
- Electrical – Where is the C wire terminal on the boiler
- Can’t get wifi thermostat to work with gas boiler
- Electrical – connect a C-wire to the electric boiler ( Slant/Fin Monitron Boiler )
- Connected C-Wire (previously unused) to thermostat, but still no power
Best Answer
Unfortunately, the Aquastat you're using does not expose a
C
terminal. The transformer is likely soldered directly to the board; so unless you're good with a solder gun, you're going to have to buy a different thermostat.The red wire attached to the
T
terminal, should be connected to theR
terminal of the thermostat. The white wire attached to theT
terminal, should be connected to theW
terminal of the thermostat. When the thermostat calls for heat, it will connect theR
terminal to theW
terminal. This will cause the coil to pull a switch closed (relay), which tells the boiler that the thermostat is cold.If you're not afraid to potentially break things, and you really want to try to get the new thermostat working. You could try to add your own
C
wire. You'll simply have to connect the newC
wire, to the other lead of the secondary coil of the transformer.Left image shows original wiring. Right image shows where the
C
terminal should be added.WARNING:
Modifying the wiring of the Aquastat will likely void the warranty, and could potentially damage the equipment. Proceed at your own risk.