Why might a double-pole breaker have the same phase on each wire lug

circuit breaker

I recently encountered a strange situation in which a double-pole breaker had failed in a spectacularly unusual way. I can say this confidently because replacing the breaker solved the problem. What I want to know is what could have possibly caused this mode of failure.

In short: Both legs of the double-pole breaker appeared to be on the same phase. I have no idea how this could have happened because a straight breaker swap rectified (figuratively, not literally) the issue.

In long: Referring to the letters in the picture below, I measured the following voltages using my multimeter:

  • 0V A-H
  • 120V A-B
  • 120V A-C
  • 240V B-C
  • 120V A-D
  • 120V A-E
  • 120V A-F
  • 240V E-F
  • 120V A-G
  • 5V F-G

Subpanel, labeled with letters to identify test points

Of course,

  • A is the Neutral
  • B is the Hot (Leg 1)
  • C is the Hot (Leg 2)
  • D is a blade on Leg 1
  • E is a blade on leg 2
  • F is a screw-down terminal on the double-pole breaker (nominally Leg 1)
  • G is a screw-down terminal on the double-pole breaker (nominally Leg 2)
  • H is the Earth Ground

I tested points D and E as extra validation to make sure the contact springs on the double-pole breaker were in fact receiving power from separate legs. In retrospect, I should have also checked D-F, D-G, E-F, E-G, but I didn't do that at the time.

What could possibly cause the 5V F-G reading?

Best Answer

Your double-pole breaker is not switching both legs simultaneously as it should be.
The top D-F pole is connected, while the bottom E-G pole is not connected.

Whatever 240V appliance you have connected to that circuit is feeding the 'B' phase from D-F back into your G terminal.
Even with no appliance connected, capacitive coupling between the wires in that cable will fool your mutimeter.

If you had a load to neutral from both poles you would see 120V on one and 0V on the other.