I have 2 space heaters at opposite sides of my bathroom walls (facing into guest rooms). There is a wire that is easily accessible going between them thru the bathroom wall, which I have opened up right now. the space heaters are on a double 30 amp breakers (two 30amps tied together in the panel).
I would like to put a 15 amp (but I could use a 20amp or 30 amp if necessary) GFCI on the open wall to run hair appliances (not at the same time). Can I splice into that wire from one heater, to the GFCI and then back onto the 2nd heater?
The heaters are rarely used and haven't been turned on at all in a year or two.
Best Answer
Your standard receptacles must be 15A on a 15A circuit or 15A or 20A on a 20A circuit. Your plug-in appliances will all be designed for those type of receptacles (generally 15A and fit 15A or 20A).
GFCI is required for bathroom, but doesn't have to be at the receptacle - could be at the breaker.
You can't piggyback 15A or 20A receptacles on a 30A circuit (the heaters). Not allowed. Period.
You can repurpose the wires currently being used for the heaters to instead be used for 15A or 20A circuit. But to do that:
The alternative of "pull power from the heat/fan" will probably not work. If the heat (lamp and fan are basically "nothing") uses more than a few Amps (I'm not sure of the breakpoint) then you can't put receptacles on the same circuit.