Wiring – 6/3 NM-B (Non-Metallic) across the yard

conduitwiring

I would like to extend a 6/3 NM-B (Non-Metallic) ROMEX Simpull wire diagonally across my yard from basement to a wooden pole that will have the Nema 14-50 outlet. The outlet will be exposed to the elements, since it will not be in a enclosed area.

I have read many opinions around protecting the wire from physical damage, and in some cases that it is prohibited to run the wire in a conduit. Appreciate your help with code that will allow me to stretch the wire diagonally buried under the yard running some 30 ft.

It will be helpful to know the type of conduit I should use, how deep should it be buried underground and how to finally connect the wire to the outlet. the other end of this wire will be directly connected to a electrical panel with 50 AMP breaker. The panel is directly inside the front wall, therefore my plan is to make a hole and pull the wire from outside into the electrical panel.

Thanks all. I have decided to purchase the following items. Just wished to know if there are better sites who are reasonably priced. More importantly, wanted to show the items that I have selected from all your help..really appreciated![enter image description here]1

Best Answer

Cable in conduit

Say what? It's never prohibited to run a wire in a conduit. What's prohibited is running wires in too-darned-small conduit, which is a problem of the cheap. Well, in fairness, it's easy to mis-guess with cable, because a flat cable needs the same space as a round cable of the wide dimension. (because they twist).

For instance, with 1 cable in conduit, the conduit ID must be 138% of the widest dimension of the cable. 6/3UF is flat and 1.223" wide, so the conduit ID must be 1.680". That puts you into 2" conduit.

You need to use UF cable, because the cable you want to use, NM-B, is not rated for outdoor use, and lots of us have experience with NM-B cable failing outdoors.

Why even put cable in conduit?

Because cables are the only kind I have ever heard of. I didn't know there were other kinds of wiring.

Meet THWN-2 wire. It is actual wire, not cable. Like what's inside an NM-B sheath, but with insulation that's up to the task, and wire markings to make it legal to use directly. Needless to say, this packs much nicer into conduit than balky cable, only needing a 3/4" conduit (though I recommend 1" to make the pulling easier).

Also, it's a pleasure to pull, since each wire flexes independently.

Downside: THWN-2 cannot be used outside a conduit. So the entire route must be conduit.

Upside: Shallower burial depth, only 18" cover isntead of 24" for cable. Also, Rigid or IMC metal conduit only needs 6" cover - expensive, but the upside is you can trench it with a garden trowel.

Upside: smaller wire. 50A only requires #8 Copper THWN-2 instead of #6. Further, #6 Aluminum THWN-2 is also acceptable, for some cost savings, but this requires a socket which is CO-ALR rated. The breaker lugs are already aluminum rated.

Boxes at the pole

That's pretty easy. They already make a variety of outdoor boxes for mounting on poles, intended for RVs. Just use one of those.

You can get a simple one, that simply provides a receptacle.

Or you can get an RV "sub-panel", that provides a 50A, 30A, and normal common outlets all in the same panel. However, this will require installation of grounding rods on-site and a ground wire back to the panel must also be run. The ground wire deals with ground faults; the ground rod deals with lightning.

Certain applications will also require GFCI protection on the 50A circuit. If you need that, it needs to be a GFCI circuit breaker back in the main panel. Upside: the 120V socket doesn't need it now.

You come into the bottom of the box with conduit. Even if you use direct burial cable like UF, you must still use conduit for the rise from burial depth to the surface and on into the box. Remember your 6 AWG UF cable will require 2" conduit. Make sure your box has a knockout that big!