I'm rewiring an old house. It has a mix of knob and tube and Romex cable. I'm planning to remove all the knob and tube. In the basement I found 12-4 cable (Black, Red, White, White W/Red Stripe and ground) all in one junction box, neutrals all wired together and supplying different branch 120 v circuits. Inspecting it at the breaker box, it looks like both the black and red wires have been used as branch circuits on the same bus, but different breakers. From past experience I've learned 12-3 wire can share the same neutral but need to be on opposite bus. Is this the case with 12-4 wire?
Wiring – Can 12/2/2 cable be used with two circuits on the same leg with the neutrals tied together
wiring
Related Topic
- Electrical – GFCI Problem with Three-Way Switch WAS Two Switches Neutrals Only, Switched Hots Not Used
- Electrical – Wiring a ceiling fan and light switch with two three-cable wires
- Electrical – Is it acceptable to have two circuits with a shared hot but different neutrals
- Electrical – Are five conductor wire runs (two neutrals) for two circuits still considered a “multi-wire circuit” for code purposes
- Electrical – Some odd wiring in the breaker box. Is this up to code
- Electrical – Can two neutrals on different legs of the same circuit be connected together to shared neutral of ceiling fan
Best Answer
This is an unfortunately-all-too-common wiring error, even without a 12/2/2 cable to further confuse things. Most folks (even electricians) think "I'll just nut the neutrals together" since that's what works when everything in a box comes from one branch circuit, which is the case 99.9% of the time -- in the 0.1% case, such as yours, though -- this rule leads to a looped neutral, which violates 300.3(B):
and 310.10(H)(1):
This is easy to fix, though -- make sure that the neutrals in your 12/2/2 cable (white and white/red striped, or "candy cane wire" ;), are not nutted together anywhere.