My condo that was built in 1968 has an old thermostat(rheostat type) which supplies 2 thick gauge black wires of which one is live and the other isn't. This regulator is hooked up to a blower unit(fan) which is connected to a central ventilation system that brings hot or cold air to it. In attempting to upgrade to a programmable thermostat type, how would a single pole King Model ESP120-R that runs on 110v which has a set of red, black and white wires be connected to my unit's 2-wire setup?
Wiring – Can a 110v 3-wire thermostat be hooked up to a 110v 2-wire condo setup
hvacwiring
Related Solutions
Here's the installation manual for that thermostat: http://www.emersonclimate.com/Documents/White-Rodgers/instruction_sheets/0037-1558.pdf
You're right about L1 and L2, and about it not mattering which is which inside the thermostat housing. It is a single throw switch so its terminals are interchangeable.
The yellow triangle labeled "2" in the diagram is any device you want to turn off when the temperature gets too high. The installation manual uses an oil burner as an example of such a device. In your case you'd leave that switch unwired, unless you want to rig up a solenoid valve to douse your wood fire. :)
Take your thermostat back and get a refund
Your existing setup relied on the way double pole 240V thermostats work -- one leg is an ON/OFF (disconnect) function, while the other leg is thermostatically controlled. This is fine for running electric resistance heaters, and also in the case of a mechanical thermostat abusable for what the original installer did to control the fans ON/OFF and pump thermostatically.
However, an electronic thermostat like yours needs power for its own functions. While I'm not clear on how you wired it to get it to turn on at all, it certainly won't work correctly with both of its incoming hots on the same leg, in any case.
How to do things the right way
To actually control your system with a programmable thermostat, you'll need four things (and possibly a fifth if the installer was a cheapskate):
- A double relay module that mounts to a 1/2" KO and can handle the fan + pump loads (a RIBT242B with a 4" box cover works)
- A 24VAC/40VA Class 2 transformer that mounts to a 1/2" KO (such as the Functional Devices TR40VA040)
- A 24VAC (low voltage) programmable thermostat (use your favorite -- you have your pick here)
- Some 18/2 CL2 thermostat wire
- Optionally, a 4" square metal box that can be mounted as the old box was (if the old box was plastic, it likely lacks conduit KOs) and matching cover
- And basic electrical supplies (electrical tape, wirenuts) as well as the ability to hole and patch the wall
Installation is as follows:
- Turn power off at the panel
- Remove and replace the box with the 4" square metal box if the existing box does not have 1/2" conduit knockouts
- Install the transformer and relay to the box -- the relay's uncovered side needs to face the front and poke through the wall surface, and you'll need some access to the wall cavity to get at the transformer terminals and thread cable about.
- Put a hole in where you want the thermostat to go. Run two pieces of thermostat cable -- one to the transformer terminals, and the other to the relay. Mark the one that goes to the relay with a tape flag.
- Take the cable that goes to the transformer terminals and connect it to the transformer terminals: red to one (this'll be your R wire) and white to the other (this'll be your C wire). Take a third length of cable and connect it to the transformer terminals the same way, then run it to the relay.
- Mark the cable that came from the thermostat location to the relay with a tape flag, then stick both cables through one of the holes in the relay box. The red and white wires on the flagged cable go to the relay 1 and 2 coil screw terminals, respectively (red in this cable is W, and white is G). The white wire from the unflagged cable goes to the relay coil common screw terminal, while the red in the unflagged cable is capped with a wirenut.
- Wire up the thermostat as follows:
- Red from the unflagged cable goes to R or Rh
- White from the unflagged cable goes to C
- Red from the flagged cable goes to W
- White from the flagged cable goes to G
- Wire up the wires in the junction box as follows:
- The two "always hot" blacks from the wall are wired to each other, to the white wire from the transformer, and to the yellow and purple wires from the relay
- The orange and red wires from the transformer and the blue and grey wires from the relay are individually capped off
- The white neutral wires from the wall are all wired to each other, and to the black common wire from the transformer
- The red wires from the wall that control the fans are wired to the orange wire from the relay
- The black wires from the wall that control the pump are wired to the brown wire from the relay
- All grounds (bare or green wires) are connected to each other, and to a grounding pigtail to the box if the box is metal
- Put covers on the box and the relay
- Turn the power back on at the panel.
- Patch up any holes in the wall that aren't covered by something or the other.
- Program your new thermostat and enjoy!
Related Topic
- Connecting Wood/Electric Furnace to Smart Thermostat
- HVAC – Connecting Common Wire from Thermostat to Air Handler
- Electrical – Replacing old 3-wire line voltage single-pole thermostat with a 2-wire one
- HVAC Thermostat – Configuring a Two-Stage Thermostat to Manage Two Heating Systems
- Force Furnace Blower to Run on Separate Schedule to Circulate Air
Best Answer
The King Model ESP120-R is not compatible with your wiring. The third wire is the neutral, which this electronic thermostat requires to be operable. Your original thermostat functions as a temperature controlled switch, connecting or disconnecting the heat without any need for externally supplied power. Either you need a new replacement thermostat that also uses no separately supplied power, or you need to have your wiring altered.