A dryer was moved and the people put a junction box in its place. Can I run the new line by attaching to the old one using the junction box. They just disconnected it and turned off the breaker. I would like to reuse the line for another item requiring 240 power in my garage. Can this be done and still follow code?
Wiring – can a 240 dryer outlet be moved using a junction box
wiring
Related Solutions
Without being able to see the cables as they enter the cabinet; or the ability to touch or trace them, here is what I assume is going on.
Definitions:
Grounded (neutral) from the service
A typical single split phase service is made up of 3 wires. Two ungrounded (hot) conductors, and one grounded (neutral) conductor. The ungrounded (hot) conductors will connect to the main service panel through a disconnect (usually a large breaker), while the grounded (neutral) connects to the neutral lug. The neutral lug will be bonded (electrically connected) to the neutral bus bar, and all grounded (neutral) branch circuit conductors will terminate at the neutral bus.
Grounding Electrode Conductor
This conductor is used to connect the grounding electrode (ground rod, etc.), to the grounding bus in the panel. All equipment grounding conductors will be connected to this bus.
Bonding Jumper
The bonding jumper is used to bond (electrically connect), the un-energized metal parts of the panel to the grounding system.
Assumption:
Since it appears that (what I assume is) the grounding electrode conductor terminates at the neutral bus, I'm also assuming that this is the main service disconnect. This leads me to believe that the neutral and grounding buses are bonded (electrically connected). In which case, technically, grounded (neutral) branch circuit conductors can terminate at the grounding bus.
So you have two options:
Terminate the grounded (neutral) from the new circuit to the grounding bus.
Move the green wire that is terminated on the neutral bus, to the grounding bus. Then terminate the grounded (neutral) from the new circuit, to the freed up slot on the neutral bus.
Additional Information and Code Compliance:
Number of Conductors
Since this is a new circuit, it has to be installed to current code standards.
National Electrical Code 2011
ARTICLE 250 — GROUNDING AND BONDING
VI. Equipment Grounding and Equipment Grounding Conductors
250.140 Frames of Ranges and Clothes Dryers. Frames of electric ranges, wall-mounted ovens, counter-mounted cooking units, clothes dryers, and outlet or junction boxes that are part of the circuit for these appliances shall be connected to the equipment grounding conductor in the manner specified by 250.134 or 250.138.
Which in this case means installing a NEMA 14 receptacle for the dryer, and a proper grounding conductor.
You'll have to follow the dryer manufacturers installation instructions for upgrading to a 4 wire cord. For more information see this answer, and this answer.
Since you've said that you're already using 4 wire cable, you'll simply have to terminate the grounding conductor in the cable to the grounding bus in the service panel. Then connect the other end of the grounding conductor to the grounding terminal in the dryer receptacle.
Size of Conductors
You'll also want to be sure that you're using the proper size breaker and conductors. In the case of a dryer, you'll typically use a 30 ampere breaker and 10 AWG conductors (depending on the length of the run). However, you'll want to check the dryer manufacturers installation instructions to verify this.
Code may vary where you live
Yes. You are going to create a "Shared Neutral" circuit. This isn't difficult or dangerous, but you should do some labeling in the panel and the box itself. First, it looks like the receptacle is a 30A/220V grounded receptacle (the wire itself may also be 30A -typical for an electric dryer- but that doesn't matter since you are using 20A breakers and receptacles). You are going to share the neutral and ground wires for these (2) new circuits by wire-nutting the two circuits in your first location (the junction inside the GFCI).
Shut off power to the 40 amp double pole breaker.
Assuming you have a red, black, white, and green/bare wire: The red is one hot. The black is the second hot. The white is the neutral for both. The green/bare is the ground for both.
Assuming that the "red" circuit will be the GFCI at this location, connect the Red to the hot\line side of the GFCI, make a pigtailed white wire to do the same. On the load side of the GFCI, run the continuation of the circuit. Using the Black wire and another pigtailed neutral, junction these to the line that is going to the other room. To be a good citizen: Label the inside of the box "Shared Neutral". Extra points if you "tie" the two hots together with a piece of white electrical tape with some extra length so it looks like a little "flag" that says "Shared Neutral". Double extra points if you label the cover plate so that someone sees it before they make any future modifications.
Go to your panel. If you are not comfortable working in the panel, shut off the main power and probably have a friend hold 1 or 2 flashlights for you.
Disconnect the (2) hot wires from the 40 amp double pole breaker (I assume these will be red and black). LEAVE the neutral and ground in place. Remove the breaker and simply replace it with (2) 20 Amp breakers. Keep the same position in the panel OR make sure that the breakers are on OPPOSITE poles -as if they were a single 220 volt circuit. IT IS IMPERATIVE THAT THEY ARE NOT BOTH ON THE SAME POLE OR YOU RUN THE RISK OF SENDING 40 AMPS THOUGH THE NEUTRAL ON THE SAME POLE (If you need further explanation, please ask -this is the most important safety step). Some people will disagree and will say to use a 20 Amp double pole breaker. The problem with this is that it inaccurately appears to be (1) 220 volt circuit instead of (2) 110 volt circuits with a shared neutral. There is an exception to this rule below.*
LABEL The panel cover by bracketing the (2) circuit labels and write "Shared Neutral". Extra points: inside the panel, tie the (2) hots together (the red & black) with a piece of white electrical tape that says "Shared Neutral".
NOTE: You will NOT be able to split the circuit after the GFCI ...so don't think you can give GFCI protection to both circuits with (1) GFCI receptacle. If you want the other circuit to be GFCI protected, you must use another GFCI receptacle in the first location of the second (black) circuit. You also will not be able to use a single pole GFCI breaker on either circuit. You must either use (2) GFCI receptacles as above. Alternatively, you may use (1) double-pole (220volt) GFCI circuit breaker -but you should still label the circuit as "Shared Neutral".
- EXCEPTION TO THE (2) 20 AMP CIRCUIT BREAKER RULE: If you want these circuits to be AFCI protected you must use (1) double pole (220 volt) AFCI circuit breaker. You should still label the circuits as "Shared Neutral".
...That was fun to write! :D
Peace, Greg
Related Topic
- Wiring – use (share) a 120 leg of the 240 with the neutral to a 120 duplex receptacle in the same box coming off the 240 circuit breaker
- Electrical – add a second junction box to house a doorbell transformer
- Wiring – outlet next to breaker box
- Electrical – install two independent gfci outlets in one double-gang box
- Electrical advice concerning a 220v dryer outlet and circuit
- Electrical – Are all ground wires inside electrical junction box grounded
- Electrical – run THHN for separate washer and dryer circuits through the same conduit
- Electrical – Surface-mounted Electric Circuit (conduit) – do I need a junction box
Best Answer
The answer is yes if the conductors meet code.you already turned off, Remove The receptacle install a clamp in the old box for the new wire to feed the new the receptacle If Romex the putter insulation 1/4” inside the clamp and 6” wire minimum. Use appropriate sized wire-nuts and install a blank cover, put the new box where you want it , bring the wire in make sure to have at least 6” and the putter covering or insulation inside the box by 1/4” reconnect your receptacle and you are ready to plug in. Electric driers are usually #10 wire on a 30 amp breaker. Can be larger but that is normal. I usually use 4 square metal boxes with a 30 amp 1/2” raised cover . The receptacle should be a 4 wire by today’s code well and the last few cycles. Good luck.