I'm planning on running cat6 solid cable throughout many areas of my house. The best way for me to get from the basement to the second floor is through a pvc pipe my builder installed with the house that runs to the attic. I have already used this pipe to run electrical wire up to the attic so I could install my outside flood lights…..thinking ahead before I order everything will I need shielded cat6 since it is running up this pipe with the other electrical wires? Am I setting myself up for a lot of interference if I don't use shielded cat6 and grounded keystones or can I just get the wall rated riser cat6 and regular keystones? Thanks in advance!!!!
Wiring – Cat6 shielded cable or no
wiring
Related Solutions
Since you are on breakers 10 & 12 it is probably a multiwire branch circuit sharing the neutral, today's code requires handle ties if this is the case. Verify the hot feeding the light and switch. A noncontact tester may show a hot line or a phantom induced voltage. Depending on the wiring it could be a switched neutral this would be a code violation and is common in home owners doing there own wiring. The correct way would be to take the black wire that feeds the light and connect it to the black that goes to the switch, in the switch box the white wire that comes in with the black needs to be marked with paint or electrical tape a color other than white or green. The white in the light on the same cable feeding the switch needs to me marked also. Heat lamps usually take special fixtures that have high temp wires and many of the heat lamp fixtures have a maximum wattage of 300w some much less. Excess wattage lamps can be the cause for the discoloration of the insulation. The wiring needs to be evaluated and possibly repaired with proper junction boxes added. It would be a good idea to add handle ties to breaker 10-12 if it is a multiwire branch circuit. They may not have been required when the home was wired but are a good safety feature now. This or replacing the 2 breakers with a double pole breaker with 1 handle.
Wiring methods
EMT and other fixed metal conduit works as a grounding path, so you only need ground wire where the conduit is otherwise. Green, green/yellow or bare is allowed for ground wire. You don't need a ground wire per circuit, only per conduit, but it must be large enough for the largest circuit present. If bare, it must be copper outdoors.
You join a ground wire to EMT by getting a #10-32 screw and fitting it in the pre-threaded hole in the junction box. Do not use a sheet metal screw.
Conduit outdoors in conduit is outdoors. It's pretty much a foregone conclusion that your conduit will fill with water at times no matter how much you try to seal it... that's why you use THWN wire. It's designed to soak.
I have no earthly idea why someone would use solid wire in conduit, perhaps because they were buying (cheaper?) receptacles and switches not listed for stranded wire, or because they were a Romex Kaiser**. It's not worth "fixing", but I wouldn't do any more of it. It's fine for them to mix, just make sure your devices are listed to take stranded wire, and notably backstabs are not, but those are unreliable in any case.
Stranded wire costs about 5% more here. After your first time wrestling 6 solid wires and a GFCI into a 22cu.in. box, you won't mind paying 5% more.
Pulling
You have a tough pull due to the four bends, so gear up for a big one. THWN-2 is already pretty slick and lube won't be worth the unbelievable mess IMO.
The main way to prevent damage is first to thoroughly de-burr, and second prevent kinking, by watching the wires as they enter.
You cannot splice inside the conduit body. Out of the question.*
Pulling one wire at a time isn't better, it's worse. The big hank of wires will mutually help each other as well as provide added strength, whereas pulled individually the existing wires will drag on the new. Don't tape them mid-run, they need to slide a bit to go around corners.
Similar circuits
Beware of NEC 225.30, which generally prohibits running two similar circuits to a building. So having two unswitched 120VAC circuits may be disallowed. However 225.30(D) considers them dissimilar if they are switched, or a different voltage (240V). So the quickest way to clear 225.30 is put one of the circuits on a switch for some reason. Nowhere in the code does it require you to use the switch.
Marking wires
Tape is the key to marking when you don't have 8 colors of wire.
Don't distinguish wires unnecessarily: for instance the two hots going to a 240V heater or 120/240 dryer don't really need to be distinguished from each other.
In your case you need to distinguish two hots from each other, and two neutrals from each other (why? Because you might put a GFCI on one), and potentially a third spare hot.
You can put any tape color on any wire color, but it doesn't always do what you want:
Same-color tape is a little subtle, but is useful for marking. With colored tape it usually doesn't quite match the color or finish of the wire, and you can feel it.
In cable, it's easy to tell which wires are partner to a white, since they emerge from the same cable. This can drive you crazy in conduit with 4 whites coming out of a conduit. In conduit, remarking whites to a hot is disallowed (in most cases) but this cuts both ways: you can use the colored tape to distinguish different wires.
* To be pedantic about it, Code says any box/body is only a conduit body until you splice in it, then, it's a junction box... and must use junction box fill rules. This makes them way too small to splice in, in practical application. Even if the conduit body is wildly oversized for the wire, making the splice strangles the remaining capacity of the conduit, defeating the purpose "room for expansion" to oversize.
Now to be super, duper, duper pedantic, literally NEC says conduit bodies use conduit rules, but they have anything but thru wires, they are still conduit bodies but have to use special fill rules that are identical to the junction-box fill rules. And then, junction boxes use junction box rules, unless they have nothing but thru wires, then they are still junction boxes but use special rules that are identical to the conduit body rules.
** you can tell when conduit work was done by someone used to working in Romex, because they stay as close to Romex practice as possible, e.g. choose only black, white and red for the wires, and occasionally use a white for a switch loop. The old WWI German flag colors. Add green and you have the Pan-Arab colors LOL.
Related Topic
- Electrical – Cabin Wiring Plan Revisited
- Electrical – Laying conduit in preparation for electrical work? UK
- Wiring – the best practice for grounding a shielded cat 7 ethernet cable
- Multiwire Branch Circuit – How to Ensure Correct Wiring
- Wiring – How to Pull CAT6 Cable via Old RJ11 Panels
- Wiring – How to Connect CAT6 Cable to Incoming 5 Pair Telephone Cable
Best Answer
Some areas code do not allow data in the same conduit with power unless the data cable has the voltage rating of the power in that run. If you do run shielded, ground on the supply end do not ground on both ends this is how industrial plants run comm wires when in close proximity to 480V lines.