Wiring – Code question: Can electric range outlet with 6 Gage wire be exposed under surface mount box

rangereceptaclewiring

I am in the USA.

I want to change my propane stove to an electric stove.

I have read that I should put in a 50 amp outlet with 6 gauge wire.
The employee at the big-box store said I could make it easy on myself by using a surface mount box and run the wire up through the floor. Most likely, through the hole that will be left behind when I remove the gas line.

I asked if the wire needs to be protected in some fashion like with conduit.

He stated and it was not because it was not that far off the ground.

What is allowed via NEC codes?
Thanks

PS is 50 amp code on new construction for range rough in ?

Best Answer

NM, UF and SE all have specs in different chapters, but generally are all similar to the NM requirement in 2017 NEC 334.15(B) that "Cable shall be protected from physical damage where necessary by ..."

Unfortunately "where necessary" isn't well defined in the Code and is mostly up to the interpretation of the inspector. Generally a surface receptacle installed two inches off the floor, behind the range (like the instructions posted in the comments above) would not normally raise to that level if the existing hole lined up with the zone required by the stove. If it doesn't line up you could create a situation where damage is possible and protection would be needed if you don't drill a new hole. Some jurisdictions (like Chicago) have adopted additional requirements that require conduit, you can normally find local ordinances online.

Actually the code doesn't specify the exact size of circuit for a range, but the circuit has to have adequate capacity for the range used. For greater than 99% of electric residential ranges #6 copper 4-wire cable and a 50 amp breaker would normally satisfy the requirements for the range. Sometimes a 40A breaker is called out as required or allowed, but a 50A (NEMA14-50) receptacle is still used with a 40A breaker since NEMA hasn't designated a 40A configuration.