Using a Reliance 10 Circuits, 125/250 Volts, 30 Amps, 7,500 Watts, Model# 30310A unit to my panel. I was interested in running my water heater which in my panel has a two 30 amp breakers. Can I run this breaker to the dual pole 20 amp breaker on the transfer switch? Only concern is in my panel it is labeled as a 30 amp but there are no 30 amp breakers on the transfer switch so want to make sure that is not an issue.
Wiring – connect a water heater to an existing dual-pole breaker
wiring
Related Topic
- Electrical – Should I use 12/3 NM cable for a 240 volt 40 amp electric cooktop
- Electrical – 60A two pole breaker supplying a sub panel (220v) – how many amps for separate 110v legs
- Electrical – Add sub panel from transfer switch
- Electrical – use a 15A breaker for a 10A baseboard heater
- Wiring – Electrician connected new water well to house panel, but confused about wire size in generator transfer switch
- Electrical – Installing a generator transfer switch on an ITE Pushmatic panel
- Electrical – 7500 Watt Manual Transfer Switch has #10 wires, but the well pump is wired with #8
- Electrical – What’s the current input from each leg of a portable generator into the main panel
Best Answer
With having 4500W elements, the 2-pole 20A breaker will not handle the load. Based on 4500W at 240V the heater would be drawing close to 19 amps and will likely trip. You could swap the elements for 3800W which would draw closer to 16 amps. Your water will just take a little longer to heat up to temperature.