Using a Reliance 10 Circuits, 125/250 Volts, 30 Amps, 7,500 Watts, Model# 30310A unit to my panel. I was interested in running my water heater which in my panel has a two 30 amp breakers. Can I run this breaker to the dual pole 20 amp breaker on the transfer switch? Only concern is in my panel it is labeled as a 30 amp but there are no 30 amp breakers on the transfer switch so want to make sure that is not an issue.

Best Answer

With having 4500W elements, the 2-pole 20A breaker will not handle the load. Based on 4500W at 240V the heater would be drawing close to 19 amps and will likely trip. You could swap the elements for 3800W which would draw closer to 16 amps. Your water will just take a little longer to heat up to temperature.