Wiring – do I need gfci outlets for a storage room receptacles

wiring

I wired a storage room and run one 20 amp circuit for some outlets and to power the water heater and furnace does this circuit have to be gfci protected?? Or can I install regular receptacles

Best Answer

If this area is an unfinished area of a basement or crawl space then GFI protection is definitely required for ALL 120V, 15A & 20A receptacles. No exceptions, other than for fire or burglar alarm systems.

The furnace must be dedicated and should NOT have a cord and plug.

2011/14 NEC

422.12 Central Heating Equipment

Central heating equipment other than fixed electric space-heating equipment shall be supplied by an individual branch circuit.

Exception No. 1: Auxiliary equipment, such as a pump, valve, humidifier, or electrostatic air cleaner directly associated with the heating equipment, shall be permitted to be connected to the same branch circuit.

Exception No. 2: Permanently connected air-conditioning equipment shall be permitted to be connected to the same branch circuit.

If the water heater has a typical 120V cord and plug you have no choice but to use GFI protection.