Wiring – Do new wire runs in an existing ceiling need to be stapled down

code-compliancelightingrecessed-lightingremodelingwiring

I've heard some people say that code requires wiring in the wall to be stapled to framing every so often (how often?), but when you are doing a remodel, is that necessary?

I have a two story house, and would like to remove one standard dome light on the first floor ceiling and replace it with 6 recessed lights. There is about 12" of empty space between the floors, and it seems easy enough to run the wire from light to light without cutting any drywall except for the 4-5" holes required for the lights. However, there's no way I'd be able to staple the wiring down. It's just going to be loose in the ceiling, running through a small hole in the I joists every once in a while.

They sell "remodel" light cans that are made specifically so you only have to cut a hole big enough for them to fit in, so this seems like a common job. What am I missing and how can I do this job in the most correct way?

This is in Dallas, TX, single family residence.

Best Answer

If you are not removing more drywall than needed for the new recessed lights, then no per 334.30(B)(1) (assuming you are using NM cable). There are similar clauses for other flexible cable assemblies (e.g. AC/MC).

However, if you are removing drywall as part of the remodel and have access to the studs, then you do need to secure and support according the remainder of 334.30 (or similar clauses for other cable types).

From NFPA-70:2014 (a.k.a. 2014 NEC):

334.30 Securing and Supporting Nonmetallic-sheathed cable shall be supported and secured by staples, cable ties, straps, hangers, or similar fittings designed and installed so as not to damage the cable, at intervals not exceeding 1.4 m (4 1⁄2 ft) and within 300 mm (12 in.) of every outlet box. junction box, cabinet, or fitting. Flat cables shall not be stapled on edge. Sections of cable protected from physical damage by raceway shall not be required to be secured within the raceway.

(A) Horizontal Runs Through Holes and Notches. In other than vertical runs, cables installed in accordance with 300.4 shall be considered to be supported and secured where such support does not exceed 1.4-m (4 1⁄2-ft) intervals and the nonmetallic-sheathed cable is securely fastened in place by an approved means within 300 mm (12 in.) of each box, cabinet, conduit body, or other nonmetallicsheathed cable termination.

FPN: See 314.17(C) for support where nonmetallic boxes are used

334.30(B) Unsupported Cables. Nonmetallic-sheathed cable shall be permitted to be unsupported where the cable:

(1) Is fished between access points through concealed spaces in finished buildings or structures and supporting is impracticable.

(2) Is not more than 1.4 m (4 1 ⁄2 ft) from the last point of cable support to the point of connection to a luminaire or other piece > of electrical equipment and the cable and point of connection are > within an accessible ceiling