I replaced a 2-prong outlet with a GFCI, wired as shown (connected ground wire coming into the box to the metal box as well as the ground screw of the GFCI, black wire to brass terminal & white to silver). The box has no separate grounding wire and wires are only in Romex, not metal conduit. Multimeter shows hot and neutral are correct. Later, I realized I never checked whether the ground wire was actually grounded at the service box. To be code compliant, do I need to apply the "no equipment ground" sticker regardless, or only if the bare copper wire coming in is not grounded at the service box?
Wiring – Does this GFCI need a sticker for code-compliance
code-compliancegfciwiring
Related Topic
- Electrical – GFCI outlet/switch combo installation
- Electrical – Dead GFCI outlet(s), wire is live
- Adding a GFCI to an existing circuit. 2 black, 2 white wire problem
- Electrical – Wiring Options for 14/3 NM-B Cable and Two Single Pole 15 Amp Circuit Breakers
- Electrical – the correct way to wire a 3 way switch where power comes into the middle switch
- Wiring – Replacing grounded outlets with grounded metal junction box
- Electrical – Metal box grounding question GFCI outlet
Best Answer
The NEC in 250.130(C) now requires extending an Equipment Ground Conductor to the grounding system when making an extension of a two-wire circuit that does not have an EGC.