Wiring – Electrician connected new water well to house panel, but confused about wire size in generator transfer switch

wiring

Is my new, 278 ft water well, wired in safely? Electrician ran 100 ft of #6 wire from ( transfer switch out to well house control box ) & then ( 278 ft of 3 wire #12 going down csg to 1 1/2 hp pump ) 378 ft combined wire.

I checked the “Franklin Electric AIM” manual pages ( 14 & 15 ) and the calculations are shown to be acceptable @ .96 maximum allowable voltage drop to meet NEC recommendation of less than 1.0

My issue is that my “Reliance Transfer Switch )has #10 wire running from the 230 volt double pole breaker to the house panel box. So wire starts out at breaker as 4 ft of #10 wire, connected to 100 ft of #6 wire out to well house controll box, then 278 ft of # 12 ( 3 wire ) running down to pump.

The number 10 wire at transfer switch seems too small, but it comes factory wired this way, what do you guys think ?

Best Answer

If the 12AWG submersible pump wire is fine, then the 10AWG in the transfer switch is certainly fine too

A circuit's ampacity is set by the thinnest wire in the circuit. As a result, since we know that there's 12AWG wire in the circuit (going downhole to the pump), the 10AWG wire between the house panel and the transfer switch is fine.