I have an existing cooktop with a 50 amp breaker and #6 wire
Replacing cooktop with a new induction top that requires a 40 amp circuit
Is it ok to leave the 50 amp breaker box or should I swap with 40 amp breaker?
Thank you
Wiring – Existing 50 amp breaker to 40 amp
wiring
Related Topic
- Electrical – Existing 40 amp breaker with a 50 amp range spec
- Electrical – I have an induction cooktop in the island powered by a 40 amp circuit, can I spur off this to install two outlets on the side of the island
- Wiring – How to wire a sub panel from a 15 amp circuit existing run
- Electrical – 2 pole 15 amp breaker off of a 2 pole 20 amp breaker
- Electrical – Can a 40amp breaker be used safely and without issue with a 40amp device on 6AWG wire
- Wiring for new 40 amp wall oven and cooktop
- Electrical – Circuit breaker for glass cook top
Best Answer
Breakers often are tasked with two missions; protecting the conductors is always #1, and sometimes they are there to protect the equipment itself. Going from a 50A breaker to a 40A breaker is no problem from the standpoint of the protecting the conductors; you can always go down in breaker size, just never up.
So that leaves the protection for the cooktop itself. In the installation instructions (assuming you have them) or possibly on a nameplate on the unit, there should be something telling you Minimum Circuit Ampacity (abbreviated as MCA) which is addressing the MINIMUM wire size as discussed above, and there might be another listing of Maximum Over Current Protection (abbreviated MOCP) that is dealing with the protective device (fuse or breaker) that might be required in it's listing. So we cannot answer this for you other than to say "RTFM" (Read The Factory Manual).