I installed two outdoor garage lights using 14/2 MC Armorlite Cable. The lights are only 8.8 watts and have day/night sensors. I connected the wiring to a garage door opener dedicated 20 amp circuit on the ceiling. This circuit has one duplex 20 amp receptacle for the garage door opener plug. The new outdoor lights 14/2 wires are fed into that box. I now realize that the wiring is not correct. I should have used 12/2 wiring. Upon advice from a friend/electrician I replaced the 20 amp breaker with a 15 amp breaker and replaced the 20 amp receptacle with a 15 amp receptacle. Is this allowed? For safety, should I replace the wiring from the outdoor lights to the garage door receptacle with 12/2 wire?
Thank you for your advice.

Best Answer

Your friend gave you good advice. Breakers are sized by the smallest wire in the circuit. Since you added 14/2 to the circuit, a 15 AMP breaker is the maximum allowed. Replacing the receptacle was needed too. The 14/2 you installed is fine since you replaced the breaker.