Planning to use Legrand Wiremold 700 Series Metal Surface Raceway.
Couple questions:
- It is a metal box (raceway) but I don't see a green screw to ground it. Does it require grounding?
- Is it allowed to use a cable or do I need to use individual THHN wires? If the former – is it realistic to pull it through?
Best Answer
It can take its ground either from the underlying box or from a pigtail
From the installation instructions Legrand provides on their website for the 500/700 series products, I don't see any reference to an explicit grounding screw being driven, so it appears that it picks up its grounding from the underlying box being grounded. If that's not possible, the bump at the top-left that doesn't have a mounting hole in the cover corresponding to it should be tapped to accept a 10-32 grounding screw and corresponding pigtail.
...but always uses individual wires
Surface raceways are designed to be used with individual THHN wires, just like their conduit brethren. Furthermore, you have to obey the fill chart provided by the raceway manufacturer; if what you plan to run isn't a combination that's on the fill chart, you can't run it, as the irregular shapes of surface raceways mean that normal conduit fill calcs can't be used and the provisions of NEC 386.21 and the first paragraph of 386.22 apply instead: